    Default Help with the proper connectors with cast to PVC

    I'm going to try and tackle my plumbing for a basement remodel. I have two plumbing connections that I need to make, 1) replace the old shower with new for a Sterling shower enclosure. 2) Replace old bar with a new "wet" bar setup but do a proper connection not like what I found.

    Here are some pics.









    How for down do I need to go under my foundation to make the transition from cast to PVC? An even bigger question is what type of connector must be used, Fernco?

    There isn't a vent for the wet bar, so could I use one of those sink vents that gets mounted up by the top of the counter? Sorry don't know the correct name.

    Also, I found the cleanout for the main stack behind the basement bathroom wall behind the toilet. Should I put on one of the access covers that you can use to get to plumbing in drywall ceiling and such or just drywall it and remember that I may need to open that spot up if I ever need to get access there?





    If I left out more info (which I'm sure I did) just ask and I will try to answer it for you.

    Thanks!

  2. #2
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Come one guys and girls I'm sure one of you can point out what the proper transition connector would be going from CI to PVC for these two applications. My plumber went AWOL so I'm left with doing this myself!

    I'm sure its fernco type of fitting but more interested in how deep I need it in the ground?

    I have a clean out between the house and the street so I am not going to bother with the one by the toilet.

  3. #3
    DIY Senior Member asktom's Avatar
    Join Date
    Nov 2009
    Location
    Victor, MT
    Posts
    460

    Default

    Comment deleted.
    Last edited by asktom; 05-14-2013 at 05:44 AM.

  4. #4
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    THIS item from HD looks like it could work?

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Fernco is a brand name. The one most commonly thought of with the name "Fernco" is a neoprene sleeve with stainless steel hose clamps on each end. This are for underground use only. The type you must use for above ground connections is a banded coupler. These have a stainless steel band that covers the entire sleeve. Fernco makes these as well as other companies. The band must match the materials on each end. Cast sizes can vary. I would suggest a professional plumbing shop to get the proper sized coupler. You might also consider if this a DIY job. An AAV might or might not be legal where you are for venting the bar sink. The clean out should not be buried behind a wall.

  6. #6
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Thanks for the reply Gary. Yes, from searching this site I see that fernco is a brand and generic name used for these types of connectors. With my current CI ending flush with the floor if I wanted to use the banded type coupler I would need to dig down enough to expose enough of the CI for the correct fitting correct? Would I be better off using a donut type coupler or a Manhoff fitting? I found THIS previous post which is similar but working on a horizontal pipe.

    I will check on the AAV and put an access cover for the clean out then.

    Thanks

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    A donut works into a hub, but since there's no standard on the size of the hub (only the ID of the main pipe), finding the properly sized donut may be problematic as well. A banded coupler is designed to connect to the normal pipe run, not a hub. ANd, since the CI and the PVC are usually a different OD, you need to find the proper banded coupler or it could leak, or be very tight to get on.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Quote Originally Posted by jadnashua View Post
    A donut works into a hub, but since there's no standard on the size of the hub (only the ID of the main pipe), finding the properly sized donut may be problematic as well. A banded coupler is designed to connect to the normal pipe run, not a hub. ANd, since the CI and the PVC are usually a different OD, you need to find the proper banded coupler or it could leak, or be very tight to get on.
    What would you suggest to be my best approach to this?

    Should I try and remove all the concrete or whatever is around the opening to the sink drain and do the same thing for the shower as well as remove the inner 4" drain? Then I could get a better measurment on the ID of both pipes.

    Without clearing that stuff out of the way would you think both of those pipes are hub ends sticking out?

    There is at least a 2' drop in each pipe to the bottom

    Thanks

  9. #9
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default

    Not sure what goes where in your photos, but when installed the bottom of the shower drain sits below the top of the concrete, and the trap must be positioned properly below the floor. The shower drain must be 2", and there must be a vent downstream of the trap to prevent it from siphoning.

  10. #10
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Quote Originally Posted by cacher_chick View Post
    Not sure what goes where in your photos, but when installed the bottom of the shower drain sits below the top of the concrete, and the trap must be positioned properly below the floor. The shower drain must be 2", and there must be a vent downstream of the trap to prevent it from siphoning.
    Those pics are for two different areas. The vent for the shower is about maybe 4' away from the drain. The drain is up because I removed about 4~5" of shower bed under what I believe was a lead shower pan. I believe there is a trap way down below (there is about a 2' or better distance from the floor to the water) since I can see standing water and no sewer smell.

    Is there a way to check to make sure there is a p-trap somehow buried below?

  11. #11
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Unless there's a clog, standing water indicates a p-trap. Pour some water in, and if the level stays the same after a moment, it must have a p-trap and not be clogged. While the drains underneath the slab could be perfectly fine, they may also be on their last legs...it's a shame to install a new shower and shortly after find that there's a leak or the trap has collapsed because it rusted through.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #12
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Quote Originally Posted by jadnashua View Post
    Unless there's a clog, standing water indicates a p-trap. Pour some water in, and if the level stays the same after a moment, it must have a p-trap and not be clogged. While the drains underneath the slab could be perfectly fine, they may also be on their last legs...it's a shame to install a new shower and shortly after find that there's a leak or the trap has collapsed because it rusted through.
    I will try the water to see if it stays at its current level.

    Are you referring to the condition of the drains under ground based off of the picture of the shower drain? I don't have the money to fix something that isn't broken yet. I'm all for preventative maintenance but is there a compelling reason to change it out now??
    Last edited by RK05; 05-15-2013 at 10:29 AM. Reason: spelling

  13. #13
    DIY Senior Member asktom's Avatar
    Join Date
    Nov 2009
    Location
    Victor, MT
    Posts
    460

    Default

    Is the drain on your Sterling enclosure really going to line up with your old drain? That sounds too lucky to me. If not, you are going to have to bust up the concrete and at that point you will be able to see what is going on down below.

    I can't tell from your picture exactly what is going on with the connection of the lavatory drain at the floor. It looks like PVC tubular was shoved into a wiped lead joint. I think somebody faked it there. What you find when you remove the lead will determine the correct connection.

  14. #14
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Plumbing underground can last for a very long time. Sometimes it doesn't. Hopefully, yours has.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  15. #15
    DIY Junior Member RK05's Avatar
    Join Date
    May 2013
    Location
    Cincinnati
    Posts
    13

    Default

    Quote Originally Posted by asktom View Post
    Is the drain on your Sterling enclosure really going to line up with your old drain? That sounds too lucky to me. If not, you are going to have to bust up the concrete and at that point you will be able to see what is going on down below.

    I can't tell from your picture exactly what is going on with the connection of the lavatory drain at the floor. It looks like PVC tubular was shoved into a wiped lead joint. I think somebody faked it there. What you find when you remove the lead will determine the correct connection.
    It will line up because the old shower was almost 60" wide and I am putting in a 48" wide unit (72220100). I already have the backwall and one side wall framed out for the enclosure.

    That is the way I take it, that the previous owner just shoved the PVC pipe into the drain and cemented around it. I am hopefully going to get to work on the drains this weekend.

    Should I try removing the smaller 4" drain out of the larger flush CI piece? I was going to remove the stainer and look down and see how far that 4" CI goes down the larger one. Wasn't sure if I should not mess with it if I were to use a banding coupler but I don't think I will be able due to the height of that piece and my shower pan?

Similar Threads

  1. Push-fit Connectors
    By Drewski123 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 09-26-2011, 01:03 PM
  2. abs connectors
    By GoIrish89 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 08-18-2010, 09:39 AM
  3. SharkBite connectors
    By nin28 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 25
    Last Post: 02-22-2009, 10:56 PM
  4. PEX connectors
    By Mr Overkill in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-12-2007, 04:48 AM
  5. burring cast to abs connectors
    By jcrashbox in forum Remodel Forum & Blog
    Replies: 3
    Last Post: 06-27-2005, 11:12 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •