    Default Replumbing a Bath

    I've been reading this forum for a while and have found some really helpful advice and a vast amount of knowledge. Drawing on that advice, I have sketched out a design for the plumbing in my bathroom which is going to be remodeled shortly. The toilet and tub will be staying in the same locations. I will be adding a double lav and therefore the location of the existing one will change slightly. I have also attached a photo of the existing lav/toilet/main/vent connection. Some background:

    1) Total DFU's on house: 23
    2) Main line is 4" Cast Iron
    3) Existing vents through roof: 4" for main line/toilet (which I plan to replace with a 3"), 1.5" for shower and tub, 1.5 inch for kitchen.

    Basically, I would like to know if the drawings I have attached will fly. Thanks!
    Attached Images Attached Images      
    Last edited by bergs54; 05-06-2013 at 07:34 PM.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    You are under UPC plumbing code.

    The double lav needs to be a double fixture fitting, and you can use med 90's on the trap arms. Long sweep would work too there.
    You do have a long sweep below, and that's correct.

    4" allows pretty much as many toilets as you like.

    I don't understand how the lav vents are tying in. It should be above 42".

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,614

    Default

    Good plumbing practice would also install a cleanout tee beneath the double fixture fitting.
    Licensed residential and commercial plumber

  4. #4
    DIY Junior Member bergs54's Avatar
    Join Date
    Dec 2008
    Location
    California
    Posts
    10

    Default

    Thanks for the responses.

    1) As far as the long 90's on the lavs. I'm slightly confused by the code -- I thought all horizontal changes of direction had to be "a one-sixteenth (1/16) bend, one-eighth (1/8) bend, or one-sixth (1/6) bend, or other approved fittings of equivalent sweep". Are the 90's on the lavs an exception or am I misreading the code?

    2) For the lav vent connection -- sorry, my picture isn't clear. I plan on tieing the lav vent in the third picture into the 3" main vent in the fourth picture well above 42".

    3) I thought I read somewhere on the forum that it was bad practice to dump the toilet directly into the main line as I have done. Is that true? And, if so, might there be a workaround you could suggest?

    4) I was hoping to avoid a cleanout cover in the wall because the lavs are pedestal sinks, but I guess I could hide the cover with a freestanding storage unit of some sort.

    Thanks again for assistance -- it is greatly appreciated.

  5. #5
    DIY Junior Member bergs54's Avatar
    Join Date
    Dec 2008
    Location
    California
    Posts
    10

    Default

    So, based on further reading here, it looks like the toilet drain set up I had done above was incorrect because other fixtures drained in before the toilet vent. I have attached two different options which I believe fix that problem, and I was wondering if one would be preferred over the other. Thanks!
    Attached Images Attached Images  

Similar Threads

  1. A few questions during replumbing an old house
    By mikewass in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 01-26-2012, 12:25 PM
  2. As part of my replumbing project
    By svcalypso in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-07-2009, 06:04 PM
  3. Replumbing a outside pump
    By Huiced in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 07-02-2008, 09:43 AM
  4. replumbing closet flg
    By mjb30 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 12-19-2007, 06:22 PM
  5. referrals: replumbing contractors
    By inforapeek in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 31
    Last Post: 08-30-2007, 03:47 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •