    Default Hot water recirc loop issues

    Hi all,
    I have a recirculation loop in my new home. It is approx 250' start to finish--one long loop with t's off for the fixtures. Instant hot water when you turn it on. However, I'm having an issue when I turn on a faucet/shower nearby. The original faucet that was turned on is hot, and the next one is luke warm or even chilly. When I shut them both off and then turn the second one on, it's hot...here is a picture. Please let me know what you think
    Name:  water heater loop diagram.jpg
Views: 391
Size:  34.9 KB

    Thank you,
    Kendal

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    The check valve has to be on the recirulation line. When you open ANY faucet, the cold water is flowing backwards through the circulation line. Whether the water turns warm or cold depends on how fast it is flowing and how long it is run. I would also put the pump in the circulation line so any hot water used does not have to work its way through the pump, which can just exacerbate the problem.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member Kendal's Avatar
    Join Date
    Aug 2012
    Location
    Nashville, TN
    Posts
    12

    Default

    Hello,
    Thank you for the reply. So if I move the check valve as in picture below, i won't need to leave the one in the current location to prevent hot water from backing into the cold? Also, would the recirc pump go here in picture below? any other thoughts would be appreciated.Name:  water heater loop diagram updated.jpg
Views: 366
Size:  37.7 KB

  4. #4
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    You will be far better off with the recirc loop connecting to the bottom of the heater with the circulator pulling the water back to the bottom of the heater with the check valve below the circulator.

    John

  5. #5
    In the Trades Jerome2877's Avatar
    Join Date
    Aug 2009
    Location
    BC
    Posts
    384

    Default

    For what you paid for sharkbites you could have hired a plumber to do this right the first time.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    Yes to both questions, and you might also install a ball valve between the check valve and connection to the cold water line.
    Licensed residential and commercial plumber

  7. #7
    DIY Junior Member Kendal's Avatar
    Join Date
    Aug 2012
    Location
    Nashville, TN
    Posts
    12

    Default

    Quote Originally Posted by Jerome2877 View Post
    For what you paid for sharkbites you could have hired a plumber to do this right the first time.
    i did fyi...

Similar Threads

  1. Any way to have a gravity recirc loop with a tankless water heater?
    By benze in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 07-08-2012, 03:32 PM
  2. Gravity recirc loop strange problem
    By benze in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 29
    Last Post: 03-21-2012, 08:41 PM
  3. recirc loop ok can't add branch
    By den in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 01-15-2007, 06:38 AM
  4. Gravity fed recirc loop question.
    By neverman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 02-05-2006, 06:34 AM
  5. hot water recirc loop
    By shineer in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-01-2005, 08:16 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •