    Default Installing garage sink from water heater lines

    I recently had a tankless water heater installed on the outside wall of my attached garage. They re-ran the hot and supply lines from the old water heater closet in another part of the garage through the attic to the new spot on the outside wall.

    I'd like to install a utility sink inside the garage on the wall right near the tankless heater. I plan on tying the drain into the washing machine drain that is also on that wall.

    I've drawn a picture of the setup (this is like looking top-down at it - with blue/red showing the pipes coming from inside the wall):

    http://i.imgur.com/9f9qqOx.jpg

    Note: the washer supply lines do not connect to the new PEX water heater lines directly - they just happen to be in close proximity but come up from the concrete slab.

    My questions are:

    • Is it possible (and permissable) to T off of the hot output, and cold supply, that the tankless heater uses for my hot and cold water for my utility sink? The drywall is already out, and the PEX is exposed there, which would make it really easy. I could make a cut and T off of both lines, go through a couple wall studs, and hook into where I want my utility sink. I'm thinking this would be just fine.
    • Any special equipment or method I should use to tie into the washer drain line? Drains all go through my slab, so there is no adding a new drain to the system. The drain is fully vented already from the washer. If I tied into the drain below the vent I should be fine right?


    Thanks for your help!

  2. #2
    DIY Junior Member Jimmy Mooney's Avatar
    Join Date
    May 2013
    Location
    Texas
    Posts
    3

    Default

    Also here is a photo of the drain behind the dryer. Can I tie in above the P trap?

    http://i.imgur.com/zVgQoKo.jpg

  3. #3
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    Where I am, the sink drain and wet vent would need to be 2", which would require replacing the existing laundry sanitary tee.
    As a matter of personal preference, I would extend the laundry supplies and standpipe so that it is accessible when the machine is in front of it.

  4. #4
    DIY Junior Member Jimmy Mooney's Avatar
    Join Date
    May 2013
    Location
    Texas
    Posts
    3

    Default

    Fair points - but where should I Tie in the sink drain and depending on where, does the sink need a trap too?

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    I do not know which plumbing code you fall under, but I know that if you are adding a fixture to an existing plumbing system, it will require a permit and inspection almost anywhere in the U.S.
    My plumbing code allows the laundry tray connection over the washer drain connection via a vertical wet vent. Some places do not allow the wet vent, so the fixtures would require individual vents which could be tied together once they are at least 42" above the floor. Every fixture must have it's own trap to prevent sewer gas from coming back in.

    Given the nature of your questions, you might consider having a conversation with your local plumbing inspector. Some of them are better than others, but more often than not they will be happy to point you in the right direction.

Similar Threads

  1. Installing utility sink in garage -- opposite site of bathroom wall
    By Pickngrin in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 11-08-2011, 12:58 PM
  2. installing water to a garage
    By vtplumb in forum Pumps and Tanks Well Forum & Blog
    Replies: 14
    Last Post: 08-19-2011, 12:43 PM
  3. Air in faucet lines after installing new water tank and non submersible pump
    By lucymo in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 03-24-2008, 06:51 AM
  4. Relocate Water Heater to Garage - Pipe Size Issue?
    By beantech in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-05-2008, 01:46 PM
  5. Moving drain lines and water lines for pedestal sink
    By ChuckVA in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 09-10-2007, 03:56 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •