Thread: Can neutral and ground from 50A breaker be shared

  1. #1
    DIY Member rosem637's Avatar
    Join Date
    Jan 2013
    Location
    Michigan
    Posts
    38

    Default Can neutral and ground from 50A breaker be shared

    A run in 1" plastic conduit from the main panel to power a stove and a microwave. So individual conductors will be used.

    Stove is on 50A breaker with #8 wire, microwave on 20A breaker with #12 wire.

    The 1" plastic conduit will be run to a junction box and will contain four #8 conductors(red,black,white ,green) and one #12 conductor(blue).

    Question is....in the junction box can the #8 neutral and ground be connected to #12 neutral and groung conductors for the run to the microwave?

    Kind of like the diagram. Although I did not show the red and black for the stove continuing because it was getting crowded in the drawing.
    Attached Images Attached Images  
    Last edited by rosem637; 04-21-2013 at 05:23 AM.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    I guess the accurate replies here were not good enough: http://www.diychatroom.com/f18/share...-93896/index5/

  3. #3
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    I guess this post was before a answer was given on the other forum.

    "No, you cannot do that."


    Be Careful playing with electricity.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    The logical answer would be that there is NOTHING on either appliance that "needs" a #8 neutral, and the ground in a JB is often a common for everything in it.
    Licensed residential and commercial plumber

  5. #5
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by DonL View Post
    I guess this post was before a answer was given on the other forum.
    Not quite.

  6. #6
    DIY Member rosem637's Avatar
    Join Date
    Jan 2013
    Location
    Michigan
    Posts
    38

    Default

    Quote Originally Posted by Speedy Petey View Post
    Not quite.
    Yes quite.

    Answer on other forum acknowledged at 0829. This post on this forum started at 0816.

    Do not know why the concern on how and when and where this question was posted. For info it was also posted on two other forums.

    Thanks

  7. #7
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,648

    Default

    Quote Originally Posted by rosem637 View Post
    Yes quite.

    Answer on other forum acknowledged at 0829. This post on this forum started at 0816.

    Do not know why the concern on how and when and where this question was posted. For info it was also posted on two other forums.

    Thanks

    I think that a GFCI will be required for your install.

    If you start sharing Neutrals strange things can happen.


    Good Luck.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    quote; If you start sharing Neutrals strange things can happen.

    Maybe if it is going through a GFCI or you overload it.
    Licensed residential and commercial plumber

Similar Threads

  1. Odd Hot-Neutral Reverse after Ground.
    By Dr.Guacamol in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 02-08-2013, 08:52 AM
  2. Subpanel neutral/ground isolation
    By Homeownerinburb in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 01-15-2012, 04:50 PM
  3. Subpanel Neutral & Ground On Same Bar?
    By slimjim43 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 06-23-2009, 10:58 AM
  4. Shared neutral
    By beekerc in forum Electrical Forum discussion & Blog
    Replies: 26
    Last Post: 12-11-2008, 12:09 PM
  5. Neutral/ground at sub breaker panel
    By Cubey in forum Electrical Forum discussion & Blog
    Replies: 32
    Last Post: 08-18-2007, 03:17 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •