Thread: How soon can the vent from a roof drain trap go horizontal?

  1. #1
    DIY Junior Member sethamin's Avatar
    Join Date
    Feb 2013
    Location
    Brooklyn, NY, United States
    Posts
    20

    Default How soon can the vent from a roof drain trap go horizontal?

    I am replacing a storm line running to a roof drain, and it currently has no trap and connects directly to my main sewer line (combined sewer and storm lines are very common in my area). As long as I'm replacing it, I figure that I should do it properly and add a trap to it. How soon can the vent from this trap go horizontal? I assume that the "6 inches above flood rim fixture" standard doesn't apply here, since the "fixture" in question is presumably the roof, and if you were 6 inches above it, you'd already be vented.

    I'm specifically thinking of having the roof drain drop directly into a trap, then having the vent rise briefly and then jog horizontally to meet up with the main vent.

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,194
    Blog Entries
    1

    Default

    If it's on your roof, there is no reason to trap and vent it. The vent would be open air right next to it.

  3. #3
    DIY Junior Member sethamin's Avatar
    Join Date
    Feb 2013
    Location
    Brooklyn, NY, United States
    Posts
    20

    Default

    UPC 2009 states that all storm drains connected to a sewer line should be trapped:

    1103.0 Traps on Storm Drains and Leaders.
    1103.1 Where Required. Leaders and storm drains, when connected to a combined sewer, shall be trapped. Floor and area drains connected to a storm drain shall be trapped.
    Exception: Traps shall not be required where roof drains, rain leaders, and other inlets are at locations allowed under Section 906.0, Vent Termination.
    1103.2 Where Not Required. No trap shall be required for leaders or conductors that are connected to a sewer carrying storm water exclusively.
    And its definition of "Storm Drain" is:

    Building Drain (Storm) - A building drain that conveys storm water or other drainage, but no sewage.
    Granted, I take your point that it's basically being vented anyway. But a roof drain does not extend 6 inches above the roof, nor is there any guarantee that it's at least 3 feet from any window opening. So by my reading of the code, it should be trapped.

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,194
    Blog Entries
    1

    Default

    If your roof is not at the top of the building, then are you talking about a "Deck" drain?

    Vents can go horizontal when they are 6" above the flood lever of the fixture, and any other fixtures it's connected to.
    Last edited by Terry; 04-15-2013 at 03:25 PM.

  5. #5
    DIY Junior Member sethamin's Avatar
    Join Date
    Feb 2013
    Location
    Brooklyn, NY, United States
    Posts
    20

    Default

    Quote Originally Posted by Terry View Post
    If your roof is not at the top of the building, then are you talking about a "Deck" drain?
    This particular drain is for the roof of a 2 story extension off the main house (which is 4 stories). But it's part an attached townhouse, so there are neighboring buildings whose windows could be within 3 feet (even at the topmost roof - buildings are all different heights).

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,624

    Default

    Any vent for a roof drain, which is something I have never installed, would have to rise ABOVE the roof, otherwise when the drain gets plugged the water would simply rise in the pipe until it could flow into the drain system through the vent.
    Licensed residential and commercial plumber

Similar Threads

  1. Distance from fixture to roof vent stack layout review (not distance from p-trap)
    By kmuddzy in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 12-01-2011, 10:21 AM
  2. Vent size for 3" horizontal drain from water closet
    By techinstructor in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 08-12-2011, 07:43 PM
  3. Shower Drain Horizontal Before Trap?
    By Wojocad in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 04-12-2011, 07:54 PM
  4. 3" trap arm - horizontal drain height change
    By Rousifier in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 02-19-2011, 08:31 PM
  5. Leaky drain vent on roof
    By rick at home in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 10-23-2007, 03:07 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •