Thread: proper breaker and wire size for gas furnace

  1. #1
    DIY Member estone's Avatar
    Join Date
    Mar 2008
    Location
    Colorado
    Posts
    70

    Default proper breaker and wire size for gas furnace

    I had a Heil gas furnace installed that will be primarily used for a/c but it does have a heat too, Model N8MSN0701716A1. I installed the electrical with a 20 amp breaker/ 12-2 wire as per HVAC installer instructions. After searching online electrical data it calls for a 15amp breaker/14-2 wire, max. unit amps 9.5. It also says max. wire length 29ft. I have the furnace installed in my attic so I'm running close to 40 ft. of wire from the basement panel to attic. I'm really sweating this and was hoping I'm ok with the 20amp breaker/ 12-2 wire. If what I went with is really a no no I guess I can rip it out and start from scratch but I was hoping I would be ok. I would appreciate your expertise. Thanks in advance!

  2. #2
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,637

    Default

    Quote Originally Posted by estone View Post
    I had a Heil gas furnace installed that will be primarily used for a/c but it does have a heat too, Model N8MSN0701716A1. I installed the electrical with a 20 amp breaker/ 12-2 wire as per HVAC installer instructions. After searching online electrical data it calls for a 15amp breaker/14-2 wire, max. unit amps 9.5. It also says max. wire length 29ft. I have the furnace installed in my attic so I'm running close to 40 ft. of wire from the basement panel to attic. I'm really sweating this and was hoping I'm ok with the 20amp breaker/ 12-2 wire. If what I went with is really a no no I guess I can rip it out and start from scratch but I was hoping I would be ok. I would appreciate your expertise. Thanks in advance!

    The Wire is fine, And the breaker is fine also.

    Do not sweat it, You can install a 15 amp breaker if it would make you feel better.
    Last edited by DonL; 04-14-2013 at 07:57 PM.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  3. #3
    DIY Member estone's Avatar
    Join Date
    Mar 2008
    Location
    Colorado
    Posts
    70

    Default

    Installing the 15amp breaker with the 12-2 is ok? I thought a 15amp breaker had to be 14-2 wire, 20amp/12-2, 30amp/10-2? Or is that just good practice?

  4. #4
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,637

    Default

    Quote Originally Posted by estone View Post
    Installing the 15amp breaker with the 12-2 is ok? I thought a 15amp breaker had to be 14-2 wire, 20amp/12-2, 30amp/10-2? Or is that just good practice?

    The wire is larger and can carry more current / power then needed for your unit, and is better than 14 gauge.

    A 15 amp breaker would trip quicker if your unit had a fault.

    The breaker is to protect the wire from over heating, and your wire is better than needed for 15 amps.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,376

    Default

    12g is the MINIMUM wire size for a 20A CB, but 12g, because it IS bigger, will have less resistance when supplying a lower current. So, based on the max length for 14g wire in the installation manual, the use of 12g is called for, and is a GOOD thing. I'd use the recommended CB size of 15A with it. CB is designed to primarily protect the wiring, not the device, so ANY CB 20A or less is good. Using a 15A is closer to the device's rating, and would also help protect the device in addition to the wiring.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    DIY Member estone's Avatar
    Join Date
    Mar 2008
    Location
    Colorado
    Posts
    70

    Default

    Thanks for all the help. I will sleep better now.

Similar Threads

  1. Sizing Kitchen Range Breaker Size & Wire Gauge
    By chuck b in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 04-27-2011, 05:05 AM
  2. Gas Furnace Fan Trips Breaker
    By plumbtired in forum HVAC Heating & Cooling
    Replies: 8
    Last Post: 12-12-2009, 04:51 AM
  3. How to change from 2 wire to 4 wire furnace
    By snuffy47 in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 06-04-2009, 05:09 PM
  4. breaker size for 12 gauge wire
    By whoazone in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 10-20-2008, 05:02 PM
  5. romex wire and breaker to use
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 17
    Last Post: 04-02-2008, 03:02 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •