    After many hours of reading code and reading old posts on this forum I've managed to design this small DWV system for a new cabin.

    Please review the following 5 images and let me know if anything appears to NOT be legal for Florida's IPC.

    The PN# referenced in the jpgs come from Charlotte Pipe's PVC DWV Dimensional Catalog
    Thanks in advance,
    Steph

    1. Overall Layout
    Name:  Overall Layout.jpg
Views: 671
Size:  48.9 KB



    2. Shower & WC Closeup
    Name:  Shower and WC.jpg
Views: 551
Size:  43.9 KB



    3. Lav & Utility Sink Closeup
    Name:  Lav and Utility Sink.jpg
Views: 434
Size:  55.0 KB




    4. Kitchen Sink Closeup
    Name:  Kitchen Sink.jpg
Views: 421
Size:  67.1 KB



    5. Vents Closeup
    Name:  Vents.jpg
Views: 305
Size:  22.8 KB
    Last edited by Terry; 04-15-2013 at 09:43 AM.

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    No, no and NO. And Florida is an IPC state. Most of your vents are flat.
    Last edited by Terry; 04-15-2013 at 09:44 AM.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    DIY Junior Member Stephanie Maps's Avatar
    Join Date
    Mar 2013
    Location
    Florida
    Posts
    8

    Default

    lol omg that is funny.
    YES ok yes Florida is IPC. Thaaaat's what i meant to say.

    And good eye Tom Sawyer, you are correct I failed to slope the horizontal runs of the vent. I can fix that. Thank you.

    Anything else here that does not met IPC florida?

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    It's not just a matter of pitch. The vents must be vertical until they are at least 42" above the floor. Your drain routing will need to be changed to accommodate the vents.

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,146

    Default

    You also will need to lose the vent tee on the utility sink. You cannot use vent components for drainage. Is also appears that the sink is on the floor, with the trap below the floor, so I am guessing that the drawing is wrong.

    I'm sure others will pipe in, as I am on my way out the door.
    Last edited by cacher_chick; 04-14-2013 at 08:35 AM.

  6. #6
    DIY Senior Member Hammerlane's Avatar
    Join Date
    Oct 2011
    Location
    Ohio
    Posts
    252

    Default

    The wye you have taking off for the stanpipe vent should be turned the other way..allows for "smoother" air flow drawn it from vents and also allows for proper draining if/when water gets into vents. But as others have said you have some flat vents also.
    Attached Images Attached Images  

  7. #7
    DIY Junior Member Stephanie Maps's Avatar
    Join Date
    Mar 2013
    Location
    Florida
    Posts
    8

    Default

    Quote Originally Posted by cacher_chick View Post
    It's not just a matter of pitch. The vents must be vertical until...
    Oooh is THAT what Tom Sawyer meant by "Most of your vents are flat." Not the he had eagle eyes and could tell that the horizontal vent pipes forming branch vents were not sloped but that leaving the Ptrap many of my vents do not go vertical nearly enough before going horizontal.

    Thank you SO much for clarifying what he meant by that.. NOW i understand is not just and slight issue of pitch but of the entire layout.

    A "flat vent' is a vent that does not meet the following-
    Name:  905.4 IPC.JPG
Views: 277
Size:  79.7 KB

    Thanks cacher_chick, now i understand.

  8. #8
    DIY Junior Member Stephanie Maps's Avatar
    Join Date
    Mar 2013
    Location
    Florida
    Posts
    8

    Default

    Quote Originally Posted by cacher_chick View Post
    You also will need to lose the vent tee on the utility sink. You cannot use vent components for drainage.
    Ok, good eye that makes sense. I'll figure out the right series of fittings to use under a double sink. I used the same (wrong) configuration on both the kitchen and utility sink. - thanks again.


    Quote Originally Posted by cacher_chick View Post
    Is also appears that the sink is on the floor, with the trap below the floor...
    Here is better perspective of the same layout. I hope it makes more sense.

    Name:  Laundry View.jpg
Views: 262
Size:  38.3 KB

  9. #9
    DIY Junior Member Stephanie Maps's Avatar
    Join Date
    Mar 2013
    Location
    Florida
    Posts
    8

    Default

    Thanks Hammerlane regarding the position of the wye on the vent of the lav sink. That is a great drawing you used to show turned the other way.. I get it!

    However, in that instance i am trying to get to the other side of the wall in that direction.. in the direction it is currently orientated. And am going up at a 45deg to avoid creating a flat vent there.. soooo even though it might not provide the smoothest airflow at this point I am merely trying to determine what is LEGAL.

    I think you are saying that although it might be legal under IPC to use wye in the manner i have it- better airflow is achieved turning the wye in the other direction.

    The flat vents I am showing on the shower and water closet are my only real concern at this point. But they are big ones.

  10. #10
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote: soooo even though it might not provide the smoothest airflow at this point I am merely trying to determine what is LEGAL.

    It is NOT legal because it goes against the flow of the drain line, and has nothing to do with "smooth air flow".
    Licensed residential and commercial plumber

  11. #11
    DIY Junior Member Stephanie Maps's Avatar
    Join Date
    Mar 2013
    Location
    Florida
    Posts
    8

    Default

    oh really?
    I had no idea. I clearly did not understand his comment the first time then. Thanks for clarifying that for me - I thought he was saying it was legal but not ideal.
    You guys are awesome!

    Just so i understand what you are saying.

    " SECTION P2607 WORKMANSHIP

    P2607.1 General.
    Valves, pipes and fittings shall be installed in correct relationship to the direction of the flow..."

    And the CORRECT direction of flow for a wye fitting is ALWAYS in the direction shown here.

    Name:  Wye Flow Direction.jpg
Views: 327
Size:  19.1 KB

    It does not matter if the wye is used for a drain or a vent, if it is horizontal, vertical or sideways. When i see a wye i should think strictly in terms of

    Name:  EXIT ONLY.jpg
Views: 265
Size:  15.1 KB

    Is that correct?

Similar Threads

  1. Does this meet code?
    By jadnashua in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 04-11-2012, 02:11 PM
  2. Does this wet vent meet code?
    By pghsebring in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 10-08-2011, 08:38 AM
  3. trying to correct WM drain, add vent and sink, and meet code
    By MichaelO in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-07-2011, 06:16 AM
  4. Requirements to meet Plumbing code in New Orleans, LA
    By mdj_remodel in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 10-02-2010, 11:13 AM
  5. Does this meet code? (sink trap)
    By chassis in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 9
    Last Post: 01-19-2006, 07:52 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •