Vent for Kitchen Sink with Large Window

Users who are viewing this thread

Stu27

New Member
Messages
22
Reaction score
0
Points
0
Location
Northern Virginia
Part of our kitchen remodel involves the addition of a large window (12 ft) with a centered kitchen sink. How might one vent the sink in this configuration? I could put an AAV in there, but because I have an existing roof vent for the kitchen sink, I'm thinking why not try and use it?

Attached are several drawings that show a vent idea that picks up the existing roof vent.
as drawn:
1-1/2 inch trap
2 inch drain
horizontal drain length is about 23 feet to existing vertical waste stack
horizontal vent run is about 6-1/2 feet
vent penetration through roof is at existing location

Do you think I'd have a chance at getting an exception for the horizontal run that's below the flood level rim of the kitchen sink? Would the cleanout in the attic and the two long sweeps downstream to the horizontal vent run help with that exception? I've kinda got tunnel vision, stuck on only this and the AAV idea… what other options are there?

Thanks,
Stu
 

Attachments

  • front.jpg
    front.jpg
    27.5 KB · Views: 2,127
  • side.jpg
    side.jpg
    14.8 KB · Views: 1,143
  • top.jpg
    top.jpg
    14.1 KB · Views: 1,055
  • iso.jpg
    iso.jpg
    19.8 KB · Views: 1,142
  • iso2.jpg
    iso2.jpg
    42.6 KB · Views: 1,134

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The length below the sink connection is immaterial. A cleanout in the attic would be useless. You DO need a cleanout below the sink connection's "T", and that could be used to clear any obstruction in the overhead vent. It is up to the authorities whether that offset would be acceptable, but there is no reason it should not be in this case. I have even used an "island vent" setup with the foot vent connected back to the vent through the roof.
 

Stu27

New Member
Messages
22
Reaction score
0
Points
0
Location
Northern Virginia
Thanks hj. I'll see what the inspector says about this updated setup.

I was struggling with the island vent option… keeping both the foot vent and the drain with the joist bay. It seems while the foot vent could sit in the joist bay in the basement on it's way to the nearest wall, the drain would end up below the joists and probably end up stuck at the beam on it's way to the stack, unless I really lowered the drain to an uncomfortable level below the beam.
 

Attachments

  • iso3.jpg
    iso3.jpg
    35.6 KB · Views: 1,092

Asktom

Member
Messages
745
Reaction score
32
Points
18
Location
Victor, MT
Is there a vent for the toilet that you don't show? Using the kitchen drain as a horizonal wet vent isn't going to cut it.
 

Stu27

New Member
Messages
22
Reaction score
0
Points
0
Location
Northern Virginia
Here's the detail of the as-built (1984) toilet vent. The lavatory drain is 1-1/2 inch to the wye. Virginia uses the 2009 IPC. Is this vent arrangement code compliant?
 

Attachments

  • wc vent.jpg
    wc vent.jpg
    28.1 KB · Views: 1,130

Speede541

Member
Messages
164
Reaction score
2
Points
18
Location
Oakland
...You DO need a cleanout below the sink connection's "T", and that could be used to clear any obstruction in the overhead vent...

On that note, I've got a somewhat similar situation, but with the drain offset from the sink. Since the 'T' point will be behind a dishwasher, the inspector has suggested I add my cleanout to the horizontal arm, for easier access from under the sink cabinet (rather than having to pull out the dishwasher). I'm considering either location marked '1' or '2' as opposed to the standard location '3'.

However, as HJ noted, I've been under the impression that location '3' is used to clear blockages in either direction. A cleanout on the arm would only allow my snake to make the turn to clear the drain, not the vent.

So even if the inspector is approving '1' or '2', should I install a location '3' too, in keeping with best practice?

(FYI, the entire horizontal section is running out-of-wall.)

vent.jpg
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
There is a window in the wall so that must be an exterior wall. In this area we would install the cleanout at position #3, but rotate it 180 degrees so it faced to the outside.
 

Speede541

Member
Messages
164
Reaction score
2
Points
18
Location
Oakland
There is a window in the wall so that must be an exterior wall. In this area we would install the cleanout at position #3, but rotate it 180 degrees so it faced to the outside.

Hmmm... I'm hesitant to punch through my stucco for that since the inspector isn't asking for it, though it sounds like the cleanest solution. I think I'll err on the side of caution and install two cleanouts.

Thanks, HJ!
 

Tom Sawyer

In the Trades
Messages
3,625
Reaction score
34
Points
48
Location
Maine
If the horizontal portion of the vent is 6" above the flood level rim of the sink, then it's ok. Otherwise, not.
 