Thread: Do we have a faulty foot valve?

  1. #1
    DIY Junior Member RickNAZ's Avatar
    Join Date
    Sep 2010
    Location
    AZ
    Posts
    2

    Default Do we have a faulty foot valve?

    We have three 5,000 gallon buried steel tanks that collect rainwater from our roof. Each tank has a foot valve about 12 inches from the bottom of the tank. Each tank has a ball valve that shuts off air and water flow to the main outlet pipe (1 1/2" Sched 40 PVC). We have a 1/2 HP shallow well jet pump and a large Flexcon H2 Pro pressure tank. When we primed the pump and began pumping water from one tank, the system worked beautifully! When the tank we were pulling from was nearly empty, we closed the ball valve on the empty tank and opened the ball valve on another tank. At this point, we lost prime on the pump. We attempted to reprime, but after depositing 30 gallons of water, we gave up! We went back to the original tank, primed the line with about 5 1/2 gallons of water and, again, it works beautifully! Does this indicate a defective foot valve? We don't believe we have any faulty pipes as the system was fully pressure tested over 24 hours when it was installed. Would really appreciate any help you can offer!!

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    Let the pump pressure up the pressure tank and shut off. Then close the ball valve to one storage tank and open the ball valve to the other. If the pressure falls off quickly, then the water is going backwards and out somewhere in the second storage tank. It could be a broken pipe or a bad foot valve.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,681

    Default

    A bad footvalve would only cause a loss of prime if all the water ran back to the tank and air got in the pump.

Similar Threads

  1. Waterworks, Sigma, Can't identify faulty shower mixing valve?
    By johnsas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 11-10-2013, 06:45 PM
  2. Water hammer - faulty valve?
    By mcola in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 02-09-2010, 06:35 AM
  3. faulty sprinkler valve
    By defreib in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 02-27-2009, 04:33 PM
  4. Bad foot valve
    By Guest in forum Pumps and Tanks Well Forum & Blog
    Replies: 4
    Last Post: 06-08-2008, 08:26 AM
  5. Faulty pressure regulating valve?
    By mcgoughs in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 10-17-2005, 05:57 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •