    Hello, Can someone tell me if an 1 1/4 pipe can be used to drain a lav? The drain pipe would run 4 to 5 feet ,then connect into the vertical 3 inch main waste stack. Also , because of the short distance,would it still require its own vent?

    Thanks

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,151

    Default

    In the U.S., the trap and trap arm of a lav is commonly 1-1/4", but the drain is run in 1-1/2".

    From the International Plumbing Code (IPC)
    Name:  vents.jpg
Views: 658
Size:  30.8 KB

  3. #3
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,204
    Blog Entries
    1

    Default

    The lav should have a vent before it enters any "waste" stack.

    A lav can wet vent a shower, tub or toilet, but you can not run down waste on top of it in that manner.
    Last edited by Terry; 04-01-2013 at 08:51 AM.

  4. #4

    Default

    it can be 1-1/4" drain and can be stack vented if there is no discharge upstream of where it connects to the 3" main. If there is discharge from above that connection then it does require tis own separate vent

  5. #5
    DIY Junior Member poky1234's Avatar
    Join Date
    Dec 2012
    Location
    Woodbridge Ontario
    Posts
    27

    Default

    Quote Originally Posted by mikeplummer View Post
    it can be 1-1/4" drain and can be stack vented if there is no discharge upstream of where it connects to the 3" main. If there is discharge from above that connection then it does require tis own separate vent
    Thanks for the replies guys. Mikeplumber, that is exactly what we are doing. I just needed to know if 1 1/4 is ok. This is for a custom floating boathouse that has very tight quarters and is a little unconventional. I have another question but I'll post it with a pic and drawing.

Similar Threads

  1. What is the minimum slope required for horizontal toilet drain pipe?
    By Hjgmvca in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 04-23-2012, 05:44 AM
  2. minimum size for washing machine fixture
    By mmmm in forum Canadian Plumbing Code Questions
    Replies: 4
    Last Post: 10-27-2010, 02:54 PM
  3. Drain pipe size
    By DMP in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 11-18-2009, 06:27 AM
  4. Codes minimum size and opinion
    By willl in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 07-03-2008, 06:10 AM
  5. Minimum pipe size for a toilet vent?
    By lahabra in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 12-23-2007, 02:38 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •