Thread: 4 Gang Switch Box Wiring diagram

  1. #1
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default 4 Gang Switch Box Wiring diagram

    Hey all. Other than my poor artistic skills, spelling and use of scrap paper does this plan look acceptable? This is a dedicated 15 amp circuit on a GFCI breaker (it's gonna be in a bathroom) straight from the panel using 14-2 NM. Black is hot, blue neutral, green ground.



    For the three 5 wire connections in the switch box, I was going to use Ideal 452 Wing Nuts in red for hot and neutral wires but I'm not sure if I can use those for the ground wire.

    As an alternative, can "rabbit ear" connections still be used rather than the 452 nut? Any suggestions or criticisms will be most appreciated. Thanks!

  2. #2
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Ground wire (EGC) connections are no different than any other wire connections. Never heard of "rabbit ears", but if its a listed wire splicing device,
    and has the capacity for the number and size of wires,
    it should be fine. You need to ensure the switch device yokes are grounded, which may possibly require connection to the EGC.

  3. #3
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Quote Originally Posted by kreemoweet View Post
    Ground wire (EGC) connections are no different than any other wire connections. Never heard of "rabbit ears", but if its a listed wire splicing device,
    and has the capacity for the number and size of wires,
    it should be fine. You need to ensure the switch device yokes are grounded, which may possibly require connection to the EGC.
    Thanks! Is it acceptable to pigtail the EGC to the 4 switches as long as I don't exceed each individual splice's capacity? For example:



    How's that look? Or do you have a suggestion? I'm all ears.

  4. #4
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    It's not only acceptable, it's required if you're using a plastic box. There are many ways to physically attach the wires, what you show looks fine.

  5. #5
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Thank you so much for your help. I owe ya a beer

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default

    The color of a "wire nut" is a function of its size and capacity. I have a feeling that you are going to run out of "box capacity" very quickly if you make ALL those spices you show.
    Licensed residential and commercial plumber

  7. #7
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Quote Originally Posted by hj View Post
    I have a feeling that you are going to run out of "box capacity" very quickly if you make ALL those spices you show.
    I hope not. Using pretty good size box.

  8. #8
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Push-in (Wago-style) connectors are handy for making those pesky ground connections; you can get 'em with up to 8 holes.

  9. #9
    DIY Senior Member bluebinky's Avatar
    Join Date
    Aug 2011
    Location
    Santa Clara, CA
    Posts
    354

    Default

    You can cut down on the number of wires in the switch box by going with 14-3 to one device box with two switched hots and then continuing on with 14-2 to another.

    Hope that makes sense...

  10. #10
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    Quote Originally Posted by bluebinky View Post
    You can cut down on the number of wires in the switch box by going with 14-3 to one device box with two switched hots and then continuing on with 14-2 to another.

    Hope that makes sense...
    That is the way I would do it.

  11. #11
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Quote Originally Posted by bluebinky View Post
    You can cut down on the number of wires in the switch box by going with 14-3 to one device box with two switched hots and then continuing on with 14-2 to another. Hope that makes sense...
    It does. That will save a ton of box space. Thanks.

  12. #12
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Quote Originally Posted by kreemoweet View Post
    Push-in (Wago-style) connectors are handy for making those pesky ground connections; you can get 'em with up to 8 holes.
    Gonna grab some of those too since all the stuff I'm connecting doesn't draw too many amps.
    Last edited by ChrisNJ; 03-31-2013 at 04:41 AM.

  13. #13
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by ChrisNJ View Post
    Gonna grab some of those too since all the stuff I'm connecting doesn't draw too many amps.
    You can also save lots of wire by daisy-chaining the common hot and the ground. One wire long enough to go from one switch to the next, with enough insulation removed to wrap around a screw. Not cut, continuous across the screw to the next switch.

    Very much a pain with 12 ga, but everything is a pain with 12 ga. Happily you are using 14 ga, which makes all this much easier.

  14. #14
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by ChrisNJ View Post
    Gonna grab some of those too since all the stuff I'm connecting doesn't draw too many amps.
    You can also save lots of space by daisy-chaining the common hot and the ground. One wire long enough to go from one switch to the next, with enough insulation removed to wrap around a screw. Not cut, continuous across the screw to the next switch. Don't damage the conductor.

    Very much a pain with 12 ga, but everything is a pain with 12 ga. Happily you are using 14 ga, which makes all this much easier.

  15. #15
    DIY Junior Member ChrisNJ's Avatar
    Join Date
    Feb 2007
    Location
    NJ
    Posts
    24

    Default

    Quote Originally Posted by Homeownerinburb View Post
    You can also save lots of space by daisy-chaining the common hot and the ground. One wire long enough to go from one switch to the next, with enough insulation removed to wrap around a screw. Not cut, continuous across the screw to the next switch. Don't damage the conductor.
    Will that pass inspection?

Similar Threads

  1. Please Critique My Wiring Diagram
    By eric3872 in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 02-04-2013, 07:22 AM
  2. Help with wiring diagram
    By eric3872 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 02-25-2012, 07:20 PM
  3. Cconvert 2 gang switch to 3 gang switch
    By soft in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 01-05-2012, 03:17 AM
  4. Wiring diagram for bedroom
    By oxicottin in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 11-01-2010, 05:34 PM