I just had pump and pressure tank installed at my new property now I need to wire breaker the deluxe 3hp control box and pressure switch I am confused the pump directions say different from control box. Its a Gould's 3hp pump and Gould's or Franklin deluxe control box. I see where the red yellow black go from the well my question is from my 240v breaker do I run those wires into the control box? Then from the control box the sw and l1 go to the pressure switch plus the ground. Is that right? There will be two empty slots on the switch
 

85ray

New Member
Messages
20
Reaction score
0
Points
1
Location
Seattle, Washington
On the control box I have sw,L1,L2,r,y,b that's it I might have the colors wrong I don't have box in front of me and I didn't see any markings on pressure switch
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
The switch should have four screws for four wires and two pairs of contacts. One wire from the breaker L1 goes to one side of a contact. From there it goes to the motor M1 from the other side of the same contact if no control box is used, or to the L1 of the control box. Repeat for L2/M2/L2.
 

LLigetfa

DIYer, not in the trades
Messages
7,497
Reaction score
575
Points
113
Location
NW Ontario, Canada
Here is a schematic from the Goulds service manual.

wiring.jpg
 

85ray

New Member
Messages
20
Reaction score
0
Points
1
Location
Seattle, Washington
The well guys left it there wasent a manual just a diagram. Its a deluxe 3hp controlcontrol box with a few difernt things inside but 6 connections
 

Craigpump

In the Trades
Messages
2,436
Reaction score
158
Points
63
Location
Connecticut
I don't install a lot of these deluxe boxes, but if memory serves me right you only need to use one side of the pressure switch to control the pump with the deluxe box.
 

85ray

New Member
Messages
20
Reaction score
0
Points
1
Location
Seattle, Washington
That's what I have. so if I hook the control box up like what the diagram says ill be good? The SW goes to the load contact in the pressure swich and L2 goes to the line
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
L1 and L2 from the breaker straight to the L1 and L2 in the control box. Then you can use two wires and a ground as small as #18 to go from L2 and SW in the control box to one side of the pressure switch. If the points ever go bad, you can switch the wires and use the other side.
 

85ray

New Member
Messages
20
Reaction score
0
Points
1
Location
Seattle, Washington
Thanks vavleman I thought I had to run bigger wire to the pressure switch after breakfast here I will wire that part up thanks for everyones help
 