    would like to add another ground to main panel, have plastic waterline to house[from well] the water lines underslab branch out to kitchen and bath, and to outside faucet, about 60' of copper lines altogether , all lines are in contact with the ground UNDER the 4" concrete slab,, could a ground wire from main panel be attached to copper lines for additional ground? thanks

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    Normally dry earth is not much help for grounding.
    Grounding rods go down deep enough that you find moist dirt.
    Often times copper lines are grounded or bonded in case a bare wire touches them.

    A panel should have two grounding rods, and not rely on the plumbing.
    Here, is we do a repipe on a home, we're required to have the panel grounded properly before we repipe.
    Years ago they would use the copper pipe for grounding. We had to leave about ten feet out of the foundation. Too many copper thieves now for that to work.
    Last edited by Terry; 03-25-2013 at 12:03 PM.

  3. #3
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default

    The question to ask is if you have the required ground rods for the electric service, what do you accomplish by connecting your piping to the existing system? You could if you wanted to, but there is no requirement to do so.

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    I'll also ask. WHY are you doing this? Are you assuming there is some benefit?

  5. #5
    DIY Junior Member pigrew's Avatar
    Join Date
    Oct 2011
    Location
    West Lafayette, IN
    Posts
    11

    Default

    Edited: (Removed things that I wasn't completely sure about, see jwelectric's post)

    A metal water pipe system is required to be bonded to your ground. (NEC 2011: 250.104A).

    But, these pipes wouldn't count as a ground because they are not in a permanently moist part of the soil (250.53A1) since it's pretty dry beneath your slab.

    Bonding these additional items to ground will provide you with superior lightning protection (even if they are not adding any additional "grounding"). Also, bonding them will make thing safer if a live wire ever touches the pipe. If there is rebar in your footings, it would be a good idea to bond these to your ground, too.

    So, you still need two ground rods to have sufficient ground, preferably separated by 16 feet. (or some other permissible source of a ground).

    -Nathan
    Last edited by pigrew; 03-25-2013 at 06:00 PM. Reason: Remove some wrongness

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    There is a big difference between bonding found in 250.104 and grounding found in 250.52.

    Any time one rod is driven add the second rod unless you intend to pay an engineer to prove that one rod sustains 25 ohms or less 24/7.

    Anything under a pad will not constitute a grounding electrode as Terry pointed out, not enough moisture to do any good but if it is a complete copper piping system then it is required to be bonded. Any rebar in the pad needs nothing and will provide nothing. In order for rebar to be of any value it must be in the footer and the footer must be in contact with earth.

  7. #7
    DIY Junior Member pigrew's Avatar
    Join Date
    Oct 2011
    Location
    West Lafayette, IN
    Posts
    11

    Default

    Quote Originally Posted by jwelectric View Post
    There is a big difference between bonding found in 250.104 and grounding found in 250.52.

    Any time one rod is driven add the second rod unless you intend to pay an engineer to prove that one rod sustains 25 ohms or less 24/7.

    Anything under a pad will not constitute a grounding electrode as Terry pointed out, not enough moisture to do any good but if it is a complete copper piping system then it is required to be bonded. Any rebar in the pad needs nothing and will provide nothing. In order for rebar to be of any value it must be in the footer and the footer must be in contact with earth.
    Of course, you're right. I missed the part in 250.53 that was mentioning that it has to be in a moist part of the ground. I removed a lot of what I said in my above post.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Here, regardless of whether copper water lines are under the slab, which most are, when there is a plastic water supply line to the building, the electrical panel MUST be annotated, "Plastic water main, must have approved ground rods".
    Licensed residential and commercial plumber

Similar Threads

  1. Any Toto toilet model we can use with current waterlines?
    By maggiepassel in forum Toilet Forum discussions
    Replies: 2
    Last Post: 02-17-2013, 06:29 PM
  2. crawlspce( unheated but insulated) installing waterlines and drains
    By tameria11 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 09-24-2011, 03:50 PM
  3. Pvc vs copper under patio slab
    By jeffrow in forum Irrigation / Sprinkler Forum
    Replies: 5
    Last Post: 01-05-2011, 07:23 AM
  4. Copper tubing in slab
    By dx in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 22
    Last Post: 10-11-2009, 02:01 PM
  5. Under ground copper soldering
    By charxlie in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 12-16-2005, 02:23 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •