    I have taken voltage readings and I'm getting voltages on the valve...the relay on the valve is closed so it is calling for the pump to turn on...I dont feel or hear and water running ....please help as this well feeds four houses....Being fairly new at the well game I'm trying to learn as I go...as the other houses have older people and cant get down the well house any more ...so I have to take the reins....any and all suggestions welcomed...

  2. #2
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,154

    Default

    I think you are talking about the pressure swith, not a valve. Are you getting 110V or 230V? Are you checking on the outlet side of the switch or the inlet side? If you are getting proper voltage out of the switch, then you probalby have a problem down hole. (ie. wire broke or overload in the motor tripped) Or it could be a broken pipe. You would need to check the amperage to see which one it is.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,676

    Default

    Quote Originally Posted by danl02026 View Post
    I dont feel or hear and water running ...
    If water is being drawn and the pump is not moving water you would very soon go from low pressure to no pressure. If you continue to get water albeit at low pressure, suspect a hole in the pipe somewhere.

  4. #4
    millwork specialist@home depot danl02026's Avatar
    Join Date
    Oct 2009
    Location
    dedham,mass
    Posts
    9

    Default

    I want to thank everybody that replied to my post...Because the area where the pump and tank are located.... I ended up changing the circuit breaker the running capacitor...and the pressure switch....after charging the tank with air...all is well with our well....Now I was thinking of changing out the gbreaker box and putting everything in a box the is moisture proof....for this wet location....any and all thought will be considered......thanks

Similar Threads

  1. Water hammer bouncing pressure gauge needle AFTER pressure tank fills
    By hawkhunter in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 10-27-2012, 10:35 AM
  2. Super High pressure, but pressure switch appears to work properly
    By yergnov in forum Pumps and Tanks Well Forum & Blog
    Replies: 8
    Last Post: 03-03-2009, 05:14 AM
  3. Replies: 1
    Last Post: 05-14-2008, 10:13 AM
  4. 2 Houses, 2 Pressure Tanks, 1 pump, 1 controller, 1 pressure switch pro help needed!
    By betaman in forum Pumps and Tanks Well Forum & Blog
    Replies: 12
    Last Post: 05-05-2008, 05:07 AM
  5. Water in well, pump working, can't build up pressure, but doesn't lose pressure????
    By bgnotaplumber in forum Pumps and Tanks Well Forum & Blog
    Replies: 9
    Last Post: 08-20-2007, 10:32 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •