    Default Securing a wobbly PVC stack

    I just cut the last bit of CI out of my 4 inch stack, replacing it with PVC joined with Fernco sleeves. Now there is a bit of wobble that wasn't present when the CI was locked with riser clamps. I haven't yet connected branch lines to the stack and I expect that these will reduce the wobble. But until then is there some way of clamping/securing the PVC stack? I assume that the iron riser clamps are inappropriate.

  2. #2
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    There's nothing inappropriate about riser clamps on PVC.

  3. #3
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    One thing that may be part of the problem is the "Fernco sleeves" you used to connect the PVC. Typically, the term "sleeves" implies the neoprene sleeves that are clamped on each end with a hose clamp. These sleeves are not code for above ground use for the very problem you are having. They do not provide a ridged connection. The proper sleeved connectors are called "banded couplers" which have a solid clamp the full length of the sleeve. By the way, "Fernco" is a brand name and applies to all sorts of connectors made by Fernco. All of that said, you still should use riser clamps to firm up the pipes.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    Now you know why "Fernco" sleeves are NOT allowed inside the building, either under the floor or above it. Use ProFlex, (not No-Hub couplings), or similar "banded" couplings and the riser will be rigid.
    Licensed residential and commercial plumber

  5. #5
    DIY Junior Member penobscotman's Avatar
    Join Date
    Mar 2013
    Location
    Buffalo NY
    Posts
    20

    Default

    Thanks for all the replies. I will replace the flexible (that's the problem!) couplings with the rigid banded couplings. I looked at both at HD, and it seemed to me that the flexible couplings, with 4 inches top to bottom had more bearing surface than the the banded couplings. I need to go to a real plumbers's supply.

    So it's OK to use iron rider clamps? There is no danger of over-tightening and shattering the PVC?

  6. #6
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,154

    Default

    The clamp only needs to be tight enough to hold the stack. If you don't over-tighten it, there is no danger.

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    The rubber couplings only "bearing surface" is the area UNDER the clamps, which is relatively small. You could use a 2" long hose and get the same "bearing surface" and maybe more rigidity because of less area to "flex". Do not use N0-Hub couplings because the PVC pipe is slightly larger and the couplings have to "distort" to stretch over it. Use couplings specified for, made to, the size of the PVC.
    Licensed residential and commercial plumber

  8. #8
    DIY Junior Member penobscotman's Avatar
    Join Date
    Mar 2013
    Location
    Buffalo NY
    Posts
    20

    Default

    Thanks to all who responded. I did what you said - proper Fernco shielded fitting, gently tightened riser clamp and now everything seems nice and rigid.

Similar Threads

  1. Need recommendations for a non-wobbly vanity faucet
    By sdmark in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 09-26-2011, 01:31 PM
  2. Wobbly tap knobs
    By Charles.Y in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 06-05-2009, 03:14 PM
  3. Securing a vent stack
    By jay_sfb in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 10-04-2007, 06:40 AM
  4. Wobbly Tub Spout / Diverter
    By r0x in forum Shower & bathtub Forum & Blog
    Replies: 7
    Last Post: 03-17-2007, 10:15 AM
  5. Toto tank wobbly
    By NickG in forum Toilet Forum discussions
    Replies: 4
    Last Post: 03-10-2006, 07:05 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •