    Default venting issue

    hello, im installing a new bathroom in the basement and im looking for options to vent it, i have 2 stacks coming into the bsement but both have washrooms and other attached to them on the second story and first, is it code to vent to the outside at ground lvl...or do i have to run a new stack up to attic or is there a way to attach to the stacks without wet venting ? i'm kinda stuck till i figure this out so i can continue with the drywall...all comments welcome...thks

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,415
    Blog Entries
    1

    Default

    Wet venting is for a bathroom group (shower,lav, toilet) on the same floor. Not for between floors.
    A vent from the basement typically exits through the roof, or ties in at a vent 42" above the second floor.


  3. #3
    DIY Junior Member Tricky Ricky's Avatar
    Join Date
    Mar 2013
    Location
    ontario canada
    Posts
    9

    Default

    so its against code to tie a vent into the stack at basement lvl with drains above....so i have to run a new stack to the second lvl above the other drains or a new vent to the roof. correct?

  4. #4
    DIY Junior Member Tricky Ricky's Avatar
    Join Date
    Mar 2013
    Location
    ontario canada
    Posts
    9

    Default

    also, would a 2 inch vent be good for shower sink tiolet all the way to the roof or should i enlarge the vent to 3 ?

  5. #5
    DIY Junior Member Tricky Ricky's Avatar
    Join Date
    Mar 2013
    Location
    ontario canada
    Posts
    9

    Default

    looking at it again...im going to run a 2 inch vent from the basement ..up three feet...over the bathroom which is about 6 ft..into the garage then up about 10 ft..then over about 3 ft and then up through the roof about 3 ft....does this meet venting codes and the horizontal allowences ?

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    12,415
    Blog Entries
    1

    Default

    2" will vent a bathroom group assuming you have other vents in the system to make up for the exit sizing.

    With a three bath home, I will use two 2" vents and one 1.5" vent. That's the same as a single 3"

  7. #7
    DIY Junior Member Tricky Ricky's Avatar
    Join Date
    Mar 2013
    Location
    ontario canada
    Posts
    9

    Default

    the basment bathroom (shower, sink, toilet ) will have its own stack...2 inch through the roof of the garage..nothing else will be piped on it, does that meet code...or once im in the garage should i expand to 3 inch? Im not touching the exsisting stacks. they are to hard to get at without ripping walls apart and the wife would have my head...lol
    Last edited by Tricky Ricky; 03-18-2013 at 10:01 AM.

Similar Threads

  1. Main line clogged or venting issue
    By rhino0628 in forum Drain Cleaning
    Replies: 6
    Last Post: 11-25-2009, 08:43 PM
  2. Re-venting issue
    By Armafair in forum Plumbing Forum Discussion & Blog
    Replies: 1
    Last Post: 10-31-2008, 12:19 PM
  3. Replies: 34
    Last Post: 10-22-2008, 06:49 PM
  4. Kichen Sink Venting Issue
    By Gbuilder in forum Plumbing Forum Discussion & Blog
    Replies: 4
    Last Post: 09-04-2007, 08:25 PM
  5. New tub drain gurgles... venting issue?
    By AMP in forum Plumbing Forum Discussion & Blog
    Replies: 7
    Last Post: 06-18-2006, 06:31 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •