Thread: venting second floor bathroom

  1. #1
    DIY Junior Member kevinrx1's Avatar
    Join Date
    Mar 2013
    Location
    ohio
    Posts
    3

    Default venting second floor bathroom

    Hi everone:

    Is it permissible to use a sanitary tee on it's back on a horizontal drain if it is solely for a dry vent only ( no waste ). The horizontal drain is on the second floor starting with the toilet, dry vent, then 2 fixtures downstream on wyes then down to basement (septic).

    I would prefer the wye for the vent as well but it is a 3" stack and there is no room for the wye or combo even when rolling it. The stack continues to the roof. The sanitary tee is the red arrow in the pic.

    If it is permissible does anyone know the UPC code to reference to?

    Any advice appeciated...
    Attached Images Attached Images  

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    I am not familiar with your code, but where I am the sanitary tee on it's back is strictly prohibited. So is the flat drain on the tub and the un-vented sink

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    Your sink is unvented and IS an "S" trap. The tub has a flat vent. If you have room for a "T", you should have room for a "combo", and WHY would you even consider "rolling" it? The whole concept has to go back to the drawing board or contact a plumber who knows how to do it correctly and can do it that way. Not every task is a good DIY project.
    Licensed residential and commercial plumber

  4. #4
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,935

    Default

    Just for future reference. A sanitary tee can be used in the horizontal position if the run (vertical) does not receive waste. However as HJ said, nothing there is correct. seek professional services
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,191
    Blog Entries
    1

    Default

    A sanitary tee can be used in the horizontal position if the run (vertical) does not receive waste.
    That "used" to be the case with UPC Code. But then they realized that when things are "wet vented", that often later work used that vent as a "wet" vent. Unless you open the floor up and look, who would know whether there was a wye or santee fitting?
    Again, the UPC wins!

  6. #6
    DIY Junior Member kevinrx1's Avatar
    Join Date
    Mar 2013
    Location
    ohio
    Posts
    3

    Default

    i did vent the sink to the stack so it would be dry with no waste or water - just forgot to draw it in. Below is the corrected pic. The shower trap was right at 8 feet and another plumber told me to vent it stating it would drain too slow. The only option I had was the outside wall so I tried to run a circuit type vent. So, I'm looking for suggestions as to what could/should be done?Name:  bath2.jpg
Views: 261
Size:  15.3 KB

  7. #7
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    The shower drain must be routed so that it can be vented vertically downstream from the trap. The alternative would be to wet vent it through the lavatory, but by your drawing it appears that the trap would be too far from it's vent. Without seeing the layout, the joist direction and position, and the true the distances, we can only speculate.

Similar Threads

  1. Installing new 2nd floor bathroom - raised floor?
    By jharryman in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 03-19-2014, 01:42 PM
  2. venting 2nd floor bath
    By bwc in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 7
    Last Post: 12-03-2012, 06:35 AM
  3. Venting Configuration new second floor bathroom.
    By MarcSavage in forum Canadian Plumbing Code Questions
    Replies: 1
    Last Post: 07-17-2012, 04:06 AM
  4. Need advice on venting 2nd floor bath
    By adthern in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-02-2010, 10:08 AM
  5. Venting top floor bathroom
    By canton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 08-25-2005, 07:40 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •