    Default replaced pressure switch twice, pressure in tank GOES up and water goes?

    Hey pros, etc.
    My water pressure went to zero the other day, and I found that the control box was old, very rusty and funky as was the pressure switch. Replaced both, and had water for a week.......last night after the water softener was worked on we woke up to no water. So after the obligatory angry call to the softener guy I went to the Depot and bought another switch, installed it, and the water came on, filled to 40psi,didn't want to go up any more. Then I, on the advice of Rick (softener guy) turned the well breaker off, to give the well a chance to fill up (it's a 450 foot well). in 4 hours there was no water AGAIN but now almost 50psi in the tank. It is a big tank, 63 gallons (at least--we're the second owners) so I went to the forum and read that when water goes down, and pressure tank psi goes UP, that means the bladder is bad. I turned the breaker back on, lowered the tank back to 38, and the tank is filling up, but seems to stop at 42 or so on the pressure switch gauge.
    What do you guys think?
    Scott

  2. #2
    DIY Member VAWellDriller's Avatar
    Join Date
    Sep 2012
    Location
    Richmond, VA
    Posts
    56

    Default

    Make absolute sure your gauge is good, and also check to make sure the 1/4" nipple between the pressure switch and the tank is not blocked. You should also drain tank and check the tank precharge.

  3. #3
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    If the well continues to make water but the pump cannot reach the shutoff, then you probably have a hole in the pipe. Is there a topside checkvalve or more checkvalves in the line? If there is only the checkvalve in the pump, the water would run back out the hole when the pump is turned off but multiple checkvalves will mask it.

  4. #4
    DIY Junior Member scott young's Avatar
    Join Date
    Mar 2013
    Location
    Harpers Ferry, VA
    Posts
    11

    Default hole in pipe

    sounds feasible, but how in the heck do I find a hole if the pipe is buried--if it is PVC--is that even possible?

  5. #5
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    Quote Originally Posted by scott young View Post
    sounds feasible, but how in the heck do I find a hole if the pipe is buried--if it is PVC--is that even possible?
    More often than not, a hole will develop in the downpipe inside the well casing, often from abrasion caused by movement from torque.

  6. #6
    DIY Junior Member scott young's Avatar
    Join Date
    Mar 2013
    Location
    Harpers Ferry, VA
    Posts
    11

    Default

    the original builder said he put in washers around the downpipe to protect it.....its possible, it was his house---he made them from pvc.

  7. #7
    DIY Junior Member scott young's Avatar
    Join Date
    Mar 2013
    Location
    Harpers Ferry, VA
    Posts
    11

    Default nippple blocked?

    Quote Originally Posted by VAWellDriller View Post
    Make absolute sure your gauge is good, and also check to make sure the 1/4" nipple between the pressure switch and the tank is not blocked. You should also drain tank and check the tank precharge.
    When I replaced the switch, I didnt notice a nipple----I screwed the switch right on to the pipe------there was an extra piece ( a little brass fitting with a tiny tube) inthe box--that what you mean?

  8. #8
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    The pipe you screwed it onto is called a nipple. Given their size, they can easily clog.

  9. #9
    DIY Junior Member scott young's Avatar
    Join Date
    Mar 2013
    Location
    Harpers Ferry, VA
    Posts
    11

    Default

    thanks--I cleaned it thoroughly with a tiny toothbrush before replacing the switch.

  10. #10
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    2,943

    Default

    A toothbrush cannot clean the inside of the nipple. For that you need to use something like a drillbit.

Similar Threads

  1. Replaced pressure switch still no water from well
    By TominCT in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 04-19-2011, 07:22 AM
  2. Low pressure, pump stays on - tank, pressure switch? Replace all?
    By applebach in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 04-17-2011, 04:51 AM
  3. Pressure Tank replacement - CSV, new pressure switch ? Several questions
    By LeBlanc in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 08-09-2010, 09:43 AM
  4. Flussmatic Marina vs Pressure tank and Pressure switch
    By Eddievan in forum Irrigation / Sprinkler Forum
    Replies: 3
    Last Post: 01-20-2009, 05:35 AM
  5. Replies: 1
    Last Post: 05-14-2008, 10:13 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •