    Default Softener settings

    I have done the math but I want to make sure that I am in the right neighborhood in setting my new unit up, so please let me know if there is anything that I should change...still getting my head wrapped around the dosage etc...Here are my particulars...

    1.5 cuft setup w/ ws1
    3/4" city water feed into house
    12gpg hardness
    sfr- need to figure out
    2 adults and 2 almost teenagers, Yikes
    Using 60gallons per day per person, I need to look at my bill could be higher/lower but a starting point

    Doing the math I come up with 2880/daily with 23040/week with one day reserve.

    For this unit they list the factory default settings as: salt eff - 6# - 24,200, factory setting 9# - 32,000, and max 16# - 43000

    Based on my numbers I am thinking I will go with the 6# salt eff dosage, and overide the number of days and set to 8.



    That is what I think I need to do but open for someone to show me what I am missing something or offbase...Thanks in advance!

  2. #2
    That's all folks! Gary Slusser's Avatar
    Join Date
    Aug 2004
    Location
    Wherever I park the motorhome.
    Posts
    6,790

    Default

    Their K of capacity figures are higher than you will get out in the real world with regular mesh resins.

    So they may be BSing their numbers to make it look like their equipment is better than others or... selling fine mesh with its higher pressure loss or much more expensive SST-60 resin which is regular mesh size.
    Gary Slusser Retired (= out of business)
    Click Here to learn how to correctly size or program a water softener.
    CAUTION, as of Nov 12 2013 all YouTube videos showing how to rebuild a Clack valve have an error in them that can cause damage.

  3. #3
    DIY Junior Member bishoptf's Avatar
    Join Date
    Feb 2013
    Location
    missouri
    Posts
    23

    Default

    Quote Originally Posted by Gary Slusser View Post
    Their K of capacity figures are higher than you will get out in the real world with regular mesh resins.

    So they may be BSing their numbers to make it look like their equipment is better than others or... selling fine mesh with its higher pressure loss or much more expensive SST-60 resin which is regular mesh size.
    Yeah I get that but have I done my math right and dies this look like a good starting point?

  4. #4
    DIY Senior Member mialynette2003's Avatar
    Join Date
    Nov 2010
    Location
    Ocala, Florida
    Posts
    666

    Default

    With 6 lbs salt, it will only get you 20K not 24K.

  5. #5
    DIY Junior Member bishoptf's Avatar
    Join Date
    Feb 2013
    Location
    missouri
    Posts
    23

    Default

    Quote Originally Posted by mialynette2003 View Post
    With 6 lbs salt, it will only get you 20K not 24K.
    So can you expand on why this is so I can better understand, just taking the information that is in the 3m manual.

    Here is the spec sheet - http://www.3mwater.com/media/catalog...sSpecSheet.pdf
    Last edited by bishoptf; 03-05-2013 at 04:10 PM.

  6. #6
    DIY Senior Member mialynette2003's Avatar
    Join Date
    Nov 2010
    Location
    Ocala, Florida
    Posts
    666

    Default

    It could be with upflow brining you can achieve 24K but not sure. With up flow brining, you have a higher chance of hardness leakage vs down flow brining. Also, I noticed the spec sheet calls for an 10x44 media tank for 1.5 CF of media. The standard size tank is 10x54. Either it is over packed and not much free board for expansion or it does not have under bedding. Not a good idea if on city water. Buy a 5B test kit. Set the unit to run on 24K with 6 lbs salt and test the water just prior to a regen. If it remains soft your fine. If it is hard water, you have to back down the gallon count.

  7. #7
    DIY Junior Member bishoptf's Avatar
    Join Date
    Feb 2013
    Location
    missouri
    Posts
    23

    Default

    This is what I have found - Our mineral tank offering in diameters may not be like other manufacturers of water treatment products, as we utilize a turbulator distributor tube with the mineral tank which does not require as much free board (space above the resin). This has been a standard our company has used in the mineral tank sizing for over 25 years.

  8. #8
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,707
    Blog Entries
    1

    Default

    The turbulator does use a lower freeboard. I am not a big fan of the turbulator. There is nothing wrong with them and we stock and sell them, its just in 25 years of field service, I have never seen that the turbulator actually does anything that a standard design does not do. I just took a video of a system in backwash with a natural tank. you can see the aggessive action that the resin sees without a turbulator and with a proper backwash flow control. I will try to post it this weekend if I can find the time. I have used them on water with iron issues and had the same fouling problems with and without it. Specialized resins also worked minimally better than standard resin. Regular resin cleaning seemed to be the only way to maintain the resin, but the cost of the cleaners quickly outweighs the cost of the resin. Same goes for high salting. The additional cost of salt is more expensive than the resin. Citric acid seems to be the best option. it can be bought in bulk, very cheap!

  9. #9
    DIY Senior Member mialynette2003's Avatar
    Join Date
    Nov 2010
    Location
    Ocala, Florida
    Posts
    666

    Default

    In the 23 years I have been in the water treatment industry, I have never heard of any company using a turbulator on city water. There is no need for it. The under bedding most companies put in their filters helps prevent premature failure of distributor tube caused by chlorinated water. IMO, having a turbulator or distributor tube with no under bedding on chlorinated water is asking for trouble.

  10. #10
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,707
    Blog Entries
    1

    Default

    I agree, but a lot of companies sell it to differentiate their equipment from others. It is a neat little device that only adds a very small amount of money to the cost of a system which is partially offset by the smaller tank heights lower cost, and the saving on shipping costs by not allowing the use of a gravel under-bed which save about 10-15 pounds. Fortunately, the turbulators are built very well, so I have only seen a couple of failures in my 25+ years in this industry.

    Personally, I would not use one even in water with iron.

Similar Threads

  1. ERV Settings
    By imakesawdust in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 12-10-2012, 10:35 AM
  2. Water Softener Settings & Salt/Brine Grid Question.
    By John5 in forum Water Softener Forum, problems, installation and reviews
    Replies: 47
    Last Post: 12-03-2012, 04:04 PM
  3. Recommended best settings for 6700xtr 48,000 grain water softener
    By Lost Texan in forum Water Softener Forum, problems, installation and reviews
    Replies: 9
    Last Post: 11-05-2011, 08:30 PM
  4. Water Softener settings
    By OhioTurner in forum Water Softener Forum, problems, installation and reviews
    Replies: 4
    Last Post: 07-31-2011, 02:46 PM
  5. Settings for our new Fleck 2510sxt 48,000 gr. softener w/ 1.5 cu' SST 60 resin
    By k8ie in forum Water Softener Forum, problems, installation and reviews
    Replies: 9
    Last Post: 04-08-2011, 08:12 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •