    I am going to install a 1/2 HP 4" pump in my well. Can anyone tell me the pros and cons to 115 volt Vs 230 volt.

    Thanks

  2. #2
    In the Trades Texas Wellman's Avatar
    Join Date
    Feb 2010
    Location
    SE Texas-Coastal
    Posts
    487

    Default

    Go 230V and don't even worry about 115V.

  3. #3
    DIY Senior Member VAWellDriller's Avatar
    Join Date
    Sep 2012
    Location
    Richmond, VA
    Posts
    161

    Default

    Wire sizing is the only difference in ....230 draws 1/2 the amps. Most people don't fool with 115 but either will work just fine. One other note that I just recently discovered....you can run a Grundfos 3" 1/2 hp 115 volt on a little Honda EU2000 inverter generator....you cannot run a normal 115 volt 1/2 motor on a small generator. I have a Vector 1000 watt running 2000 watt surge 12 volt inverter on the service truck for running small hand tools, and I can actually run the grundfos on that.....I was amazed.

  4. #4
    DIY Senior Member craigpump's Avatar
    Join Date
    Apr 2012
    Location
    ct
    Posts
    712

    Default

    The only time we install a 115 volt pump is when we do a jet to submersible conversion and the homeowner won't get an electrician in to upgrade the circuit to 230 volts.

  5. #5
    Moderator valveman's Avatar
    Join Date
    Mar 2006
    Location
    Lubbock, Texas
    Posts
    4,156

    Default

    "Reduced-voltage starters may not be required if the maximum recommended cable length is used. With maximum recommended cable length there is a 5% voltage drop in the cable at running amps, resulting in about 20% reduction in starting current and about 36% reduction in starting torque compared to having rated voltage at the motor. This may be enough reduction in starting current so that reduced-voltage starters are not required." Franklin AIM manual

    You would be surprised how the above helps when running from a generator. You can start much larger pumps with a generator if you don't "up-size" the wire. Also starting the pump against a closed valve greatly reduces the starting current. So using the "longest length of the smallest wire possible" plus starting the pump against a closed valve will reduce the inrush current so a smaller generator can start a regular pump.

Similar Threads

  1. 230 volt question
    By Duke76 in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 07-19-2009, 05:41 PM
  2. Swithching 240 Volt, 2 leg circuit
    By Dave Williams in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 01-01-2008, 11:12 PM
  3. 230 Volt?
    By AZ Contractor in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 09-24-2007, 09:29 AM
  4. 12 volt DC/Solar pump
    By dscogin in forum Irrigation / Sprinkler Forum
    Replies: 2
    Last Post: 07-24-2007, 08:54 AM
  5. 12 volt transformer
    By Snafu34 in forum Electrical Forum discussion & Blog
    Replies: 13
    Last Post: 06-28-2007, 08:58 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •