    I'm installing a washer and dryer in my bathroom during a complete remodel of the bathroom. I'm planning on tying into the bath tub drain and installing a trap in the back wall of the bathroom for the washer. It will be about 2-3 feet above the floor and uses 2 inch ABS. The Y is going to be placed after the tub drain trap. Is this the proper way to do this?

    Code:
    Here's a rough diagram 
                                   
                                   Washer drain tube
                                   |
                                   |
                                   |
                                   Trap for washer
                                   |  
                                   |    
                                   | -------------------------|
                                                                        |
    Tub Y for overflow and drain---Tub Trap------Y for washer----
    The tub drain links up to a larger ABS pipe heading into the basement and another heading off to (I'm assuming) the sink.
    Last edited by maniac78; 11-24-2004 at 12:14 PM.

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Have you checked to see if in your jurisdicition a WM must have a pan under it with drain connected? How are you venting the dryer? Is the dryer 220 volt or gas? ( Gas would not be allowed in the bedroom>)

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default drain

    Your drawing is not as clear as you probably intended it, but from what we can see you have no vent for the washer trap and therefore it is not a proper installation.

  4. #4

    Default

    But isn't the drain for the tub vented already? Or do you think that adding another fixture to a drain will overload it and therefore I need an additional vent? If so then can I use an auto-vent?

    Both appliances are electric. The dryer is 220 volt. I had an electrician add seperate circuits for each.

  5. #5
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    The trap for the tub should remain vented.

    You can wye off for the washer, that should have a p-trap and be vented also. So what you have are two seperate traps, each vented. The vents can be combined at 6" above the highest "flood level" of the fixtures.

    Without the venting, one fixture can affect the other.
    When my brother moved into a log cabin that had plumbed the washer in line with the kitchen sink. Everytime the washer ran, it backed goo into the sink.

    Replumbing to code fixed that.