    Default circulating pump on return continuously running on gv90+

    Hello,

    I recently replaced a 20+ year boiler with a Weil-Mclain GV90+. My installer used the existing setup where there was a circulating pump on the return that was continuously circulating into the boiler. The boiler is having problems heating some of the radiators on the 2nd and 3rd floors so I decided to read the boiler manual:

    http://www.weil-mclain.com/en/multim...ler_manual.pdf

    and in the circulators section i found the following paragraphs:

    "Never install another pump in series with the GV90+ boiler. Forced flow can cause improper operation of the boiler controls. Substantial property damage could result.

    Failure to comply could result in unreliable performance and nuisance shutdowns from insufficient flow."

    It looks like the the boiler was installed incorrectly? Does the pump need to be removed or relocated?


    Thanks!

  2. #2
    DIY Junior Member ted33014's Avatar
    Join Date
    Feb 2013
    Location
    Ontario
    Posts
    2

    Default

    I should mention that the GV90+ comes with its own System Circulator. I believe it is a Taco 007.

Similar Threads

  1. Injector Pump Running Continuously (not switching off)
    By thanksFORtheHELP in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 06-19-2011, 05:50 PM
  2. Replies: 3
    Last Post: 01-03-2011, 01:29 PM
  3. Oversized circulating pump repercussions?
    By Macman in forum HVAC Heating & Cooling
    Replies: 11
    Last Post: 01-28-2009, 03:00 PM
  4. Hot Water Circulating Pump
    By SAnsari in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 01-13-2009, 07:03 AM
  5. Well Pump Running Continuously (Would This Cause Ground Saturation)
    By invisible-man in forum Pumps and Tanks Well Forum & Blog
    Replies: 1
    Last Post: 06-24-2008, 08:44 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •