Thread: Blue Green stain- From coil?

Hybrid View

  1. #1
    DIY Member thinkly's Avatar
    Join Date
    May 2008
    Location
    Kansas
    Posts
    41

    Default Blue Green stain- From coil?

    Name:  mms_picture.jpg
Views: 172
Size:  30.3 KB

    I am pretty HVAC illiterate, so please forgive me. What is this green type stain that appears to have leaked out of the "coil" and has left a blue green stain. Also it has made a rust spot on the furnace. The picture is taken looking down on the furnace from the coil. Thanks for any help.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,443

    Default

    Corroding copper (the coil's tubing is likely copper) produces a compound that color. You should check the drain pipe and the drain pan under the coil and make sure it does drain properly. It looks like the drain is plugged, overflowed, and that's the reason for the staining on top of the furnace. Long term, that could rust out things inside, decreasing the life of the thing. Also, if the drain line does not have a trap in it, one should be added. I have one similar to this...it makes it easy to clean things out with the supplied (on some versions) brush.
    Attached Images Attached Images  
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    As pointed out by JAD, the plug right above the pipe is a secondary drain...which should NOT be plugged. It is meant to act as a tell-tale if the primary drain is clogged, to prevent the drain pan overflow which apparently you are experiencing.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,443

    Default

    FWIW, there are two sets of two drain plug holes in the case to allow for either vertical or horizontal airflow. Since yours (should) be configured for upflow, I think they're using the wrong drain plugs, and the coil may not have been installed properly for your application. This would make the pan inoperable if it isn't installed properly as well.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by jadnashua View Post
    FWIW, there are two sets of two drain plug holes in the case to allow for either vertical or horizontal airflow. Since yours (should) be configured for upflow, I think they're using the wrong drain plugs, and the coil may not have been installed properly for your application. This would make the pan inoperable if it isn't installed properly as well.

    I think in his photo, "UP" is on the LEFT, so I interpret that he is using the right set of holes, just should open up the secondary port.

  6. #6
    DIY Member thinkly's Avatar
    Join Date
    May 2008
    Location
    Kansas
    Posts
    41

    Default

    Quote Originally Posted by jimbo View Post
    I think in his photo, "UP" is on the LEFT, so I interpret that he is using the right set of holes, just should open up the secondary port.
    Sorry for the confusing photo. Hope this helps. Name:  Untitled-1 copy.jpg
Views: 118
Size:  65.0 KB PICTURE TAKEN LOOKING DOWN ON THE DRAIN PIPE FROM ABOVE. What do you mean by open up the secondary port? I have never done PVC work, so maybe hamstrung here?

    Can I just go the where the pvc enters the floor drain and try to suck it out with shop vac etc?
    Last edited by thinkly; 02-11-2013 at 01:29 PM.

  7. #7
    DIY Member thinkly's Avatar
    Join Date
    May 2008
    Location
    Kansas
    Posts
    41

    Default

    Quote Originally Posted by jimbo View Post
    As pointed out by JAD, the plug right above the pipe is a secondary drain...which should NOT be plugged. It is meant to act as a tell-tale if the primary drain is clogged, to prevent the drain pan overflow which apparently you are experiencing.
    Are you referring to my picture or his?

Similar Threads

  1. Blue stain in tub. Not acid water. Electrolysis?
    By boerdoc in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 03-03-2009, 11:33 PM
  2. Blue/Green oxide on pipe feeding HVAC unit
    By AJTSheppard in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 10-22-2008, 06:31 PM
  3. Green Stain in Kohler Toilets (1 year old)
    By proxybox in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 02-21-2006, 01:11 PM
  4. copper pipes covered in green/blue dust
    By lyle in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 12-06-2005, 10:51 AM
  5. Blue/green stains on pipes/clothes
    By cdschm in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 10-15-2005, 09:00 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •