    Default Is this shower drain to code?

    Can a shower drain be added to this existing washing machine drain?

    The pink pipes in the diagram would be new?

    Thanks

    Mike

    Name:  UpstairsBathShowerDrainPipes.jpg
Views: 695
Size:  11.2 KB

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    No, when the WM was running, it would siphon the proposed shower drain dry. EACH trap needs a vent. Depending on how big that pipe is, you might be able to do it IF you added a vent, but a WM drain line can be problematic. You don't want sudsy water getting pumped into your shower!
    Last edited by jadnashua; 02-05-2013 at 08:18 PM. Reason: changed drain to vent....
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks for the answer.
    I know very little about drains but I'm trying to remove a shower wall that contains a vent. (the green wall in the diagram)

    Would there be too many bends in the line to bring the shower drain to the vent in wall A and from there back to the current drain below the green wall?

    Name:  UpstairsBathShowerDrainPipes1.jpg
Views: 554
Size:  17.1 KB

  4. #4
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Would this setup work?
    Attached Images Attached Images  

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,157

    Default

    If you look at your first drawing you will note that the vents are vertical. They have to be that way to ensure that no waste ever backs into the vent and stays there.

  6. #6
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks.
    I'm starting to understand.
    I do have a sink drain with a vent that is vertical but it would be a 6ft run from the shower trap.
    Is that too far?

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    The vent must come off of the trap arm before the waste turns down, and must be within 5' with a 2" pipe. It must go vertical before it can go horizontal.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  8. #8
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks I think it is going to work.

  9. #9
    Plumber Sean Beck's Avatar
    Join Date
    Jun 2013
    Location
    Toronto, Ontario, Canada
    Posts
    48

    Default

    Quote Originally Posted by Mikeiii View Post
    Can a shower drain be added to this existing washing machine drain?

    The pink pipes in the diagram would be new?

    Thanks

    Mike

    Name:  UpstairsBathShowerDrainPipes.jpg
Views: 695
Size:  11.2 KB
    You could say that the drain upstream of the proposed pink drain could be a wet vent, and providing that that drain is 1.5", then it can take up to 2FU (fixture units) which would cover the washing machine. You just have to make sure the distance from the trap of the shower to the proposed wet vent would be more than 2 x the diameter of the drain pipe (so probably 3 inches).

  10. #10
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,157

    Default

    Most codes only allow wet venting bath groups, so venting past the laundry would not be permitted.

  11. #11
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,214
    Blog Entries
    1

    Default

    Right.
    No inspector would allow a washer in any wet vent situation. That washer would suck the trap so fast it wouldn't be funny.

  12. #12
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,946

    Default

    Not only that but the washing machine rain has to drain into a 3" or larger horizontal or vertical branch.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  13. #13
    DIY Junior Member frodo's Avatar
    Join Date
    Jun 2013
    Location
    Mississippi
    Posts
    12

    Default

    can you do this ..
    the tree of liberty must be refreshed from time to time with the blood of patriots and tyrants
    herzlichen gluckwunsch zum dd ich bin uberrascht wen nicht alies da findet

Similar Threads

  1. Code requirement for custom shower drain?
    By Stealthfox in forum Shower & bathtub Forum & Blog
    Replies: 7
    Last Post: 03-17-2013, 12:33 PM
  2. Shower Drain Size and Code
    By centurion in forum Shower & bathtub Forum & Blog
    Replies: 15
    Last Post: 02-19-2012, 06:27 AM
  3. shower drain & p trap code question
    By nc8861 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 07-20-2008, 05:19 PM
  4. Code for Steam Shower Line/Drain
    By colbymom in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 07-08-2008, 04:16 AM
  5. drain code HELP!
    By Racerxjling in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 10-25-2004, 06:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •