Thread: Is this shower drain to code?

  1. #1
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default Is this shower drain to code?

    Can a shower drain be added to this existing washing machine drain?

    The pink pipes in the diagram would be new?

    Thanks

    Mike

    Name:  UpstairsBathShowerDrainPipes.jpg
Views: 140
Size:  11.2 KB

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    19,196

    Default

    No, when the WM was running, it would siphon the proposed shower drain dry. EACH trap needs a vent. Depending on how big that pipe is, you might be able to do it IF you added a vent, but a WM drain line can be problematic. You don't want sudsy water getting pumped into your shower!
    Last edited by jadnashua; 02-05-2013 at 08:18 PM. Reason: changed drain to vent....
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer

  3. #3
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks for the answer.
    I know very little about drains but I'm trying to remove a shower wall that contains a vent. (the green wall in the diagram)

    Would there be too many bends in the line to bring the shower drain to the vent in wall A and from there back to the current drain below the green wall?

    Name:  UpstairsBathShowerDrainPipes1.jpg
Views: 154
Size:  17.1 KB

  4. #4
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Would this setup work?
    Attached Images Attached Images  

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    2,670

    Default

    If you look at your first drawing you will note that the vents are vertical. They have to be that way to ensure that no waste ever backs into the vent and stays there.

  6. #6
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks.
    I'm starting to understand.
    I do have a sink drain with a vent that is vertical but it would be a 6ft run from the shower trap.
    Is that too far?

  7. #7
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    19,196

    Default

    The vent must come off of the trap arm before the waste turns down, and must be within 5' with a 2" pipe. It must go vertical before it can go horizontal.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer

  8. #8
    DIY Junior Member Mikeiii's Avatar
    Join Date
    Jan 2009
    Location
    California
    Posts
    13

    Default

    Thanks I think it is going to work.

Similar Threads

  1. Code requirement for custom shower drain?
    By Stealthfox in forum Shower & bathtub Forum & Blog
    Replies: 7
    Last Post: 03-17-2013, 12:33 PM
  2. Shower Drain Size and Code
    By centurion in forum Shower & bathtub Forum & Blog
    Replies: 15
    Last Post: 02-19-2012, 06:27 AM
  3. shower drain & p trap code question
    By nc8861 in forum Plumbing Forum Discussion & Blog
    Replies: 5
    Last Post: 07-20-2008, 05:19 PM
  4. Code for Steam Shower Line/Drain
    By colbymom in forum Plumbing Forum Discussion & Blog
    Replies: 0
    Last Post: 07-08-2008, 04:16 AM
  5. drain code HELP!
    By Racerxjling in forum Plumbing Forum Discussion & Blog
    Replies: 4
    Last Post: 10-25-2004, 06:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •