    Default Running Wires in Conduit inside a wall

    Here is the situation.

    I am in the middle of remodeling a bathroom on the upper floor of a split-foyer. It is right above the unfinished laundry, where the electric box is situated (the lower level is the basement and above the first floor is an unfinished attic). I have taken everything off down to the framing. In the corner of the bathroom there is a roughly 3x4 enclosed passageway that runs straight from the laundry to the attic. In it, the builders ran the main A/C air duct to upper floor, as well as the flue from the Gas Water heater and Furnace. This chase is enclosed by framing all around and has metal sheeting on the top (to attic) and bottom (to basement).

    I had this idea about running 2 conduits from Basement to attic to “future-proof” the place and get ready for future remodel ideas! Conceptually, I would use one to fish electric wires (I was thinking of the usual 14/2 NM-B and 12-2 Romex NM/B which have been ran elsewhere) and the other to run low-voltage wires (RG-6 and Cat 5e. perhaps speaker wire). The purpose of the conduits would have been to simply have a path (it will be about a 9 foot run) between the attic and the basement) to simplify future wiring.

    As I look into this, there seems to be more to it than the electrician at the local home improvement store conveyed. I am hoping readers here have better ideas:
    1. What other approach would you use (if not what I am trying to do) to accomplish the same purpose? (note: the rest of the house if finished and I won't get the same straight shot to laundry on any future project)

    2. If going the conduit route, I was recommended to use 2 x 1inch PVC 10 foot conduits.
    a. Would the scenario be OK for low-voltage wires;
    b. I have come across things like fill % (seems to be 40% for 1” pvc pipe) for NM wire in conduit. Apparently, there is danger of overheating. But this would barely give me 2 runs and defeat the purpose of what I had in mind! Ideas?
    c. If I run a conduit, what could I do at the two ends for:
    i. Fire protection;
    ii. Prevent Insects from crawling it;
    iii. Preventing heat loss from basement to attic
    Thank you

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,154

    Default

    Romex is a specific brand name for NM cable. NM is not rated for and should not be used inside of conduit. When installing wiring in conduit one would use individual conductors rated THNN/THWN. There is a maximum number of conductors that could go into each size of conduit, but once there are over 3 conductors they must be de-rated.

    Any holes drilled between floors for pipe/wire/conduit/etc. must be sealed with fire-rated caulking.

    What you are trying to do is not a bad idea, but given that NM cable can easily be pulled through a finished interior wall at any point in the future, it might not be worth bothering.

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Install a small panel upstairs for future use and install the feeders now. Install at least three 1 inch conduits with boxes on each end for the low voltage stuff.

  4. #4
    Electrical Contractor Jim Port's Avatar
    Join Date
    Aug 2009
    Location
    Maryland
    Posts
    156

    Default

    Quote Originally Posted by cacher_chick View Post
    Romex is a specific brand name for NM cable. NM is not rated for and should not be used inside of conduit. .
    NM is allowed inside of conduit by the NEC and is sometimes required to be protected by a conduit.

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,154

    Default

    Jim, there is not a question in regards to the appropriateness of sleeving a single NM cable for protection where it becomes necessary. I do not believe that it is appropriate for distances going between floors in a building.

    I am not an electrician, but I am quite sure you will not find a table in the NEC regarding conductor fill or derating NM cable in conduit. If I am mistaken, please show me what I have overlooked.
    Last edited by cacher_chick; 01-31-2013 at 07:44 PM.

  6. #6
    DIY Junior Member Andi.M's Avatar
    Join Date
    Jan 2013
    Location
    Virginia
    Posts
    3

    Default C

    I wanted to thank everyone who has replied.

    Quote Originally Posted by jwelectric View Post
    Install a small panel upstairs for future use and install the feeders now.
    Interesting thought! So, guess how many electric circuits I will likely need for the remodel and pull lines from the electric box to a small panel in the attic, so I will be ready when the time comes...

    Would I connect the circuits to the main electric panel and leave their circuit breakers off at this point?

    In the attic, would I simply use standard wire connectors to terminate / cover each circuit?

    What type of "electric box" would go in the attic? Something like the following?
    http://www.homedepot.com/h_d1/N-5yc1...1#.UQuNivLVBdg

    Should I drill holes in the floor and ceiling joists to pull these wires or am I allowed to simply use the chase I mentioned earlier. That way, I would simply make a hole in the metal sheets (less that 1/16" thick) on the top and bottom of the chase to run the wires. Seems a lot easier and would not damage the wood. I just wonder why the builder would not have done so. Is there any concern?

    Quote Originally Posted by jwelectric View Post
    Install at least three 1 inch conduits with boxes on each end for the low voltage stuff.
    Use 3 x 1-inch PVC conduits with conduit boxes /w Gasket, like the following? http://www.homedepot.com/h_d1/N-5yc1...3#.UQuN2_LVBdg

    How would I "seal" (or would I) the hole on the boxes that remains open? (again to prevent bugs, fire concerns, air flow)

    Am I allowed to simply use the chase I mentioned earlier? That way, I would simply make a hole in the metal sheets on the top and bottom of the chase and run the conduits. Seems a lot easier and would not damage the wood.=Is there any concern?

    Thank you

  7. #7
    DIY Junior Member Andi.M's Avatar
    Join Date
    Jan 2013
    Location
    Virginia
    Posts
    3

    Default

    Quote Originally Posted by cacher_chick View Post
    There is a maximum number of conductors that could go into each size of conduit, but once there are over 3 conductors they must be de-rated.
    Does this apply to low voltage "smart wires" in a conduit, as well? Any source for how to calculating "de-rating" ?!
    Thank you

  8. #8
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    use this for the electrical circuits. Install a feeder on a 50 t0 100 amp breaker
    http://www.homedepot.com/webapp/cata...gry=Search+All

    Use the metal box for the communication cables

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,432

    Default

    You could install the panel in the attic, but you might be able to make room in a closet that would make checking and resetting them easier. Now, if all's well, that isn't a normal situation. There are code requirements on access both to the sides and above and in front of the panel, so that could limit where you might put one. But, there'd probably be room in a walk-in closet, should one of those be in the plan. With a remote panel, you only need to run a four-wire cable from the main (ground, neutral, and two hots). The size of that depends on the size of the CB at the main you feed it with.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    That sounds like good advice all but the closet part. Panels are not allowed in closets

  11. #11
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    quote; Panels are not allowed in closets
    Maybe not, but I find a lot of them IN closets, as long as they have the proper clearance in front of them.
    Licensed residential and commercial plumber

  12. #12
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Let me correct myself. It is perfectly fine to put a panel in a closet, bathroom, or even a shower. What you can’t do is put overcurrent such as fuses or breakers in that panel in either of these places no matter the clearances.

    240.24(D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
    (E) Not Located in Bathrooms. In dwelling units, dormitories, and guest rooms or guest suites, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.

  13. #13
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    Quote Originally Posted by jwelectric View Post
    Let me correct myself. It is perfectly fine to put a panel in a closet, bathroom, or even a shower. What you can’t do is put overcurrent such as fuses or breakers in that panel in either of these places no matter the clearances.

    240.24(D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
    (E) Not Located in Bathrooms. In dwelling units, dormitories, and guest rooms or guest suites, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.
    This certainly would rule out most garages.

  14. #14
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by ActionDave View Post
    This certainly would rule out most garages.
    maybe or maybe not

Similar Threads

  1. running cat6s inside plastic conduit with 120v
    By cmozment in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 02-27-2011, 08:45 AM
  2. MN-B, 12-3/GRD inside 2" PVC conduit
    By Ford2001 in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 09-21-2009, 07:28 PM
  3. Can overhead service wire be run inside conduit?
    By leejosepho in forum Electrical Forum discussion & Blog
    Replies: 22
    Last Post: 10-15-2008, 05:12 PM
  4. Conduit size vs. number of wires
    By brosnt1 in forum Electrical Forum discussion & Blog
    Replies: 1
    Last Post: 09-06-2007, 06:31 AM
  5. pump wires inside the supply piping?
    By Raucina in forum Pumps and Tanks Well Forum & Blog
    Replies: 13
    Last Post: 09-07-2006, 05:29 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •