    The package heat pump in question require two circuits. Is it usual for an electrician to run one circuit large enough to run both to a loadcenter by the package unit and then take two branch circuits off of there? And then use this load center as the equipment's service disconnect?

    If I understand this correctly(and please let me know if you think I don't)...

    Run 2-#2 75c THW and 1 - #8 bare in 2" pvc conduit from the outside loadcenter/meter base on a 100amp breaker

    to

    say an Eaton 125 Amp 4-Space/Circuit CH Type Main Lug Loadcenter

    and and from this, run a whip with the two circuits with wire sizes and MOCPs per manufacturer's specs

    Name:  Heat pump SD.jpg
Views: 110
Size:  15.6 KB
    Last edited by mrbeing123; 01-28-2013 at 01:41 PM.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    #2 is good for 90 amps and the #8 can be a green insulated it does not need to be bare
    Last edited by jwelectric; 01-29-2013 at 02:42 AM. Reason: spelling

  3. #3
    DIY Junior Member mrbeing123's Avatar
    Join Date
    Dec 2012
    Location
    Louisiana USA
    Posts
    19

    Default

    Quote Originally Posted by jwelectric View Post
    #2 is good for 90 amps
    #2 Cu is rated at 115a per table 310-16. #2 al 75c is rated for 90a. or am I missing something?

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by mrbeing123 View Post
    #2 Cu is rated at 115a per table 310-16. #2 al 75c is rated for 90a. or am I missing something?
    U R correct

Similar Threads

  1. Building Service Disconnect question
    By gtmoy in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 01-21-2012, 03:08 PM
  2. Water heater service disconnect question
    By turnsouth in forum Electrical Forum discussion & Blog
    Replies: 12
    Last Post: 08-16-2010, 12:26 PM
  3. Service Disconnect Fuse Contacts
    By dave9600 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 01-11-2009, 06:39 AM
  4. choosing a disconnect for heat pump...
    By Randyj in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 07-11-2008, 02:18 PM
  5. Heat Pump Service
    By catzilla in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 05-02-2007, 04:22 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •