    I've just gotten my new Burnham Alpine 150 boiler going in the last few days and I'm trying to get it set up properly. My installer's attitude is pretty much that the standard settings are just fine and I'm happy to experiment with them on my own. I'm in Newton, Mass and my antique house has old-fashioned cast-iron radiators. The outdoor temp since I have installed has been in the 5-20F range.

    I have several questions, but let's start with the "smoke" plume, which is more than I expected. It seem to me that if the unit is condensing, there should be little moisture in the exhaust to cause a plume. At the moment I have a setpoint of 139F and return temp maxing out around 130 degrees. Each cycle tends to run about half way indicating "Max efficiency" but seems to drop that indication when the return temp hits about 127. I'm still getting a pretty good plume.

    What conditions contribute to the amount of plume?

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The dew points the last few days have been below zero, so any moisture left will create a condensation cloud. May be normal. Although, it does sound like you have a much bigger boiler than required. If it is keeping the house comfortable with the outside temps we've been having with only 139-degree water, it's probably too big, maybe by a factor of two and likely more, which means it will never reach max efficiency. If properly sized, it's likely when it's near zero F out, it couldn't keep the house warm unless the water temp was higher.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Retired Software Engineer gypsydoctor's Avatar
    Join Date
    Jan 2013
    Location
    Newton, MA
    Posts
    5

    Default

    Thanks, Jim.

    I had the unit installed in a big hurry because my oil tank sprung a leak at the worst time. Let's just say the planning was not done optimally. I suspect your guess of "too big by a factor of two" is pretty accurate.

    I changed the "Central Heat Maximum Modulation" from 5500 to 4850 RPM, the value for the 105 MBTU model. The manual says to change this setting if the unit is too big for the amount of radiation. It did not seem to make much of a difference. Do you think this affects things much? I suppose it affects the resolution of the modulation since the minimum speed is fixed. Maybe I will try a lower setting.

    I have a three-speed Grundfos circulator on the secondary loop (one zone) set to medium. How does this setting affect the return temp? Should I use low speed?

    Do you know how the burner meters the gas flow to match the air supply as the fan changes speed?

    Mark
    Last edited by gypsydoctor; 01-25-2013 at 08:35 PM.

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    If the water goes through slower in a secondary loop, it should return cooler since it has more time to release heat and there's less heat going in. I do not know how the gas valve modulates to maintain a proper air mix.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Extraordinary weather causes strange things to happen, as : http://pittsburgh.cbslocal.com/2013/...y-power-plant/

  6. #6
    Master Hot Water Mpls,MN BadgerBoilerMN's Avatar
    Join Date
    Mar 2011
    Location
    Minneapolis
    Posts
    285

    Default

    The more it runs the more you save and the more comfortable you will feel.

    A modulating, condensing boiler (ModCon) is the perfect match for cold cast iron radiated houses. Here in Minnepolis we regularly cut fuel bills in half. The plume is by-and-large, water vapor, and a normal byproduct of any fuel conversion, likely at 100F vs. your old oil boiler at 450F +, which may very well "burn" with a clear flue discharge but in reality is much dirtier with excessive SOx, NOx and particulates never found in a gas-fired condensing boiler.

    Most of the time your radiator will run below body temperature and only in the coldest weather get to say 140F depending on original construction and subsequent updates in insulation, window and weather stripping.

    You should have the unit set up by a trained professional used a combustion analyser before playing with controls.

  7. #7
    Retired Software Engineer gypsydoctor's Avatar
    Join Date
    Jan 2013
    Location
    Newton, MA
    Posts
    5

    Default

    Quote Originally Posted by jadnashua View Post
    If the water goes through slower in a secondary loop, it should return cooler since it has more time to release heat and there's less heat going in.
    Since there are primary and secondary loops, wouldn't slowing the secondary loop just let more of the flow of the primary loop get back to the boiler, increasing the return temperature?

    Aside from the efficiency issue, I find that things are much quieter with the circulator set at Lo speed. At Medium and Hi speeds I get noise through the floor into the room above, and also some water noise from the radiator in the bedroom.
    Last edited by gypsydoctor; 03-14-2013 at 09:15 AM.
    Mark Dionne
    Retired software engineer

  8. #8
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,715

    Default

    Quote Originally Posted by gypsydoctor View Post
    Since there are primary and secondary loops, wouldn't slowing the secondary loop just let more of the flow of the primary loop get back to the boiler, increasing the return temperature?

    Aside from the efficiency issue, I find that things are much quieter with the circulator set at Lo speed. I get noise through the floor into the room above, and also some water noise from the radiator in the bedroom.
    At minimum fire you're kind of stuck with that truth (another reason why you don't want to oversize the sucker 3x like this one probably is.) But if it's in a modulating region it will vary. Either way, you have to design the correct flow for both loops to optimize efficiency.

Similar Threads

  1. Replies: 4
    Last Post: 01-27-2012, 03:30 PM
  2. Rotate exhaust vent on new propane boiler install?
    By thebordella in forum HVAC Heating & Cooling
    Replies: 2
    Last Post: 12-10-2011, 02:09 AM
  3. health hazards from "toilet plume" aerosol
    By Alan Muller in forum Toilet Forum discussions
    Replies: 31
    Last Post: 11-05-2009, 02:16 PM
  4. Toilet Advice for people with medical conditions
    By EKDEAN in forum Toilet Forum discussions
    Replies: 2
    Last Post: 08-04-2009, 06:12 PM
  5. Back boiler & oil boiler to twin copper cylinder
    By sheen in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 12-07-2006, 04:34 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •