    Default volume question

    I have a 3000 sq ft home that when we flush a toilet on one side of the house, or run the washing machine ,there is a major pressure loss everywhere else. I checked the water pressure on one of the garden hose faucets and it is around 60 psi . I assume that there is a volume problem. The house is around 20 years old and in Gold River , ca. Alot of my neighbors had line breaks and had to take the plumbing overhead because the builder buit this addition (2500 homes) on a bed of cobble.
    It has gotten worse since they change water service and installed new water meters.
    There are no asbuil;ts for this community. It is an unincorporated area of Sacramento County , which obviously the builder got away with anything. I went to the county who told me only the architect would have the plans . I went to the Architect and he said it was too long ago and he dosen't have plans and that the buider changed his mind so much during construction that lord knows what is under my house.
    Certainly would of like to have known this fact before I bought but now I am stuck.
    Can anyone tell me how to proceed in checking out why there is such pressure loss just by flushing one toilet.

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    FIrst, make sure that the shutoff to the house is fully open. Then, if you have a PRV, it may have failed. Then, take a look where the water comes into the house and try to determine what kind of pipe it is, and what size it is. Then, get back with your observations. A bad prv can show that, but you may or may not have one. Galvanized piping eventually rusts and can choke the volume off prior to rusting through, so if there's any of that, that may be the issue...all it takes is a small section to do that.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    You need to check the pressure where the line enters the house WHILE the water is flowing in one of the faucets.
    Licensed residential and commercial plumber

Similar Threads

  1. Moen exact temp volume contol valve question
    By J_Racer in forum Shower & bathtub Forum & Blog
    Replies: 0
    Last Post: 07-24-2012, 10:00 PM
  2. water volume question
    By monkeybrains in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 8
    Last Post: 11-12-2010, 07:47 PM
  3. Multiple shower head supply volume question
    By Photovor in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 01-12-2010, 03:00 PM
  4. Question on installation methods regarding pressure and volume/
    By joebartolucci in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-14-2009, 04:05 PM
  5. Pump volume and pressure question
    By djdixon1995 in forum Pumps and Tanks Well Forum & Blog
    Replies: 3
    Last Post: 01-18-2008, 06:00 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •