    Default Collapsed flexible tubing used for the drain line on the condensate pump

    After 3 month of use, I just noticed that about a 10 Ft section of the flexible tubing used for the drain line on the condensate pump has collapsed. From the furnace to the ceiling, it is flatter than a pancake. It must be too soft to maintain its shape. This can't be normal and will not drain well.

    Can anyone tell me how my contractor should fix the problem and why this even happened?

  2. #2
    DIYer, not in the trades LLigetfa's Avatar
    Join Date
    Feb 2011
    Location
    NW Ontario, Canada
    Posts
    3,688

    Default

    I use PEX.

  3. #3
    DIY Senior Member DanMcD's Avatar
    Join Date
    Jun 2005
    Location
    Dayton, OH
    Posts
    121

    Default

    Well, the HVAC guy replaced the entire piece of 3/8 inch flexible vinyl flexible tubing that ran from my condensate pump to the laundry room tub. The entire piece was flat as can be. He said he never saw anything like it in his 20 years on the job.
    I wondered if when I chlorinated my well, the chlorine somehow did this…but that is hard for me to believe.

  4. #4
    DIY Senior Member DanMcD's Avatar
    Join Date
    Jun 2005
    Location
    Dayton, OH
    Posts
    121

    Default

    Terry Love,

    Can you tell me how that picture by my username gets displayed when I post a message. I like it, but I never posted a picture to use.

  5. #5
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Terry picked the photo based on your location. You see mine is baskets of apples. Well, in reality, I don't think any apples in Yakima, WA were ever picked in baskets, in fact bushel boxes haven't been used for years. But, the point is of course, apples and Yakima are very closely connected.
    Last edited by Gary Swart; 01-17-2013 at 12:56 PM.

  6. #6
    DIY Senior Member DanMcD's Avatar
    Join Date
    Jun 2005
    Location
    Dayton, OH
    Posts
    121

    Default

    Well, for you HVAC folks out there, as it turns out, my furnace contractor had twice used the wrong quality 3/8 vinyl tubing.

    The stuff for HVAC use that they were suppose to use is made by a company called Diveristech. This is thicker wall tubing. They used:

    Diversitech

    7—38P

    C1011EZ 3/8 x Ĺ

Similar Threads

  1. Where to buy flexible plastic tubing?
    By grizz in forum Pumps and Tanks Well Forum & Blog
    Replies: 6
    Last Post: 06-06-2012, 08:52 AM
  2. Backup from main line through condensate drain
    By navels in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 09-09-2009, 03:46 PM
  3. Replumbing drain for my A/C condensate line
    By ocbob in forum Remodel Forum & Blog
    Replies: 2
    Last Post: 06-03-2007, 08:30 AM
  4. Condensate drain line as trap prime
    By michael-thomas in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 5
    Last Post: 12-23-2005, 06:11 AM
  5. Flexible Copper Tubing
    By Beachcomber in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 12-13-2004, 11:35 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •