Thread: Question on Fleck 7000 water softener 64k grin

  1. #1
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default Question on Fleck 7000 water softener 64k grin

    what's the difference between fiberglass vs mineral tank? I see different vendors supply these 2 tanks as 12 x 48 and 12 x 52 for 64k grin system.


    In additon: My current setup were using 3/4" piping. I could have using the flex connectors for easy installation, but I'm worry the 3/4" piping will limited the water flow rate.

    The main piping to house were 1.25". Should I re-piping to 1" pipes instead? I'm about the purchase the softener, but needs the info before I order the system.

    Maybe I should have giving more infor:

    My current water softener is a GE Smartwater Profile 40k system with 1" male threads. Somehow the installer has using the 3/4" copper pipes to connect between softener and house's main 1.25" pipes. I can feel the water pressure drops when 2 showers run at same time. This has bothering me the last 10 years.... Finally the water softener broke down!!!

    Now, it is the chance to correct all the problem. It is good that I have decided on the Fleck 7000 64k system. I don't mind to hire a professional to install the system, but I need the info on correct size bypass connection to get with the new softener.

    As I mention ealier, I can use a flex connector for simple installation over the exiting 3/4" piping, but I don't want to face the same problem I had for last 10years. Will a 1" piping helps? Or stay with 3/4" piping since the Fleck 7000 has better internal high flow valves compares with GE?

    many thanks in advance

  2. #2
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Mineral tanks are "fiberglass" tanks. They are polyethylene inner shells with a fiberglass wrapping, then epoxy coated.

    The 12x52 is a better choice for a 2 cu. ft. system, the 12x48 is slighly small for this much media. Both are commonly used but the 12x52 is preferred.

    As to you plumbing size, code does not allow for a reduction in pipe size. Water velocity is the key issue here for pipe size considerations. Internal piping of a system is an engineered item specifically designed to accomodate a flow velocity exceeding 10 FPS, so internal manifolds will usually have an exception to the pipe size rule. Also, inspectors do not know whats inside of a system, they only know what they can see.

    I see no reason not to simply get a 2 cu. ft. 7000 w/ the proper 1-1/4" connectors. You may have to have a plumber install it, but it will be done right and to code. (hopefully)

    Stainless Falcon flex connectors are available in 1-1/4", you would only need to sweat on a couple of MIP adapters to the existing plumbing.

    Since you are in Orange County California, you will have copper plumbing, Fleck has 1-1/4" sweat connectors available at a reasonable price pt#41243-01 or 1-1/4" plastic threaded connectors pt#40565-01. Anybody you order the system from should have these parts available. Dont forget, you need to order 2 pieces.

  3. #3
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Many thanks Dittohead!!!

    I'll order the system today. I think I'll have to order the plastic bypass in either 1" or 1-1/4" to accomendate flex connectors.

  4. #4
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    The 7000 only has 1 bypass, it is a 1-1/4", the plumbing connectors are what make it the different size. See the attached picture for details.Name:  bypass.jpg
Views: 950
Size:  59.4 KB

  5. #5
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Thanks once again Dittohead.

    I am getting the 1-1/4" in plastic not brass sweat. I recall a online seller mention the flex connector required plastic connector, correct?

    Or....

    I'll probably skip the flex connection. (not sure which is better option..) I think I'll order:

    Tank Color Option:Almond
    Insulating Jacket:NO Insulating Jacket
    Brine Tank Size:18x33 Round Brine Tank 0
    Res-Care Feeder:NO Res-Care Feeder
    Resin Media Option:Hi-Capacity Resin - 8% Crosslink
    Distributor Tube:With 32MM HI-FLOW Distributor
    Turbulator Option:NO Turbulator 12x52 Tank
    Plumbing Connection:BYPASS, Noryl 1-1/4" Male NPT
    Drain Tubing:WITH Drain Tubing - 10 Ft.

    I assume the above will come with pt#40565-01 1-1/4" MNPT

    In addition: I will also order the brass sweat separately since there's no upgrade feaures on seller's website. But... which one should I get?

    1. Connector Assembly, 1" x 1-1/4" Brass Sweat w/O-Ring (2-Pack) - 41242-01

    or

    2. Connector Assembly, 1-1/4" x 1-1/2" Brass Sweat w/O-Ring (2-Pack) - 41243-01


    Dittohead, the part # you gave were #2, is that the right ones?

    thanks
    Last edited by silversaver; 01-15-2013 at 12:00 AM.

  6. #6
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Hi Dittohead,

    Can you send me the cheat sheet setting? I prefer good water quality over salt saving

    hardness 21gpg
    iron none to very low
    manganese none to very low
    chlorine 0.7ppm

    Family of 3 adults + 1 baby with 3 full bathrooms. The water usuage is about 220 gallons per day on average base on my current water softener.

    The new water softener is Fleck 7000 SXT 2 cu ft with 32mm districbutor using 1-1/4" copper pipes.

    Many thanks

  7. #7
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Name:  7000 2 email.jpg
Views: 875
Size:  86.3 KB

    Set H to 21, the rest will remain the same. Congrats on the new system!

  8. #8
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Thanks Dittohead,

    I actually bought another unit for my partner same configuration.

  9. #9
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Got the system installed. Press and hold the up and down arrow to enter the setup screen. It only allow me to set regen time, hardness, DO and RC. How do I enter the other setup screen?

  10. #10
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    set the time to 12:01 PM, wait 10 seconds, then press the up and down arrow buttons for 5-8 seconds, you are now in master programming.

    Post a picture of the installation. Who did the install for you?

  11. #11
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Jason did. His setting is little different as yours so I like to adjust it

    PS. Ah I see... you must set the time to 12:01pm first... no wonder..

    Name:  photo.jpg
Views: 872
Size:  35.4 KB
    Last edited by silversaver; 01-22-2013 at 03:42 PM.

  12. #12
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    That is a nice install. It is unlikely you will ever notice a flow restriction with 1-1/4" copper pipe feeding a house. The 7000 is a great match for that application as well. The all black system is nice looking too. I have never been a big fan of the blue or beige systems.

  13. #13
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    The black system looks pretty nice. Just one question nf your cheat sheet. Is RR set to 5 min enough to wash off the salts? I mean the rapid rinse time.

    By the way, I am experience water flow drop with only 2 fraucets on. very strange... any idea? The water pressure in the house is 70psi +



    thanks

  14. #14
    Water systems designer, R&D ditttohead's Avatar
    Join Date
    Jan 2012
    Location
    California
    Posts
    1,712
    Blog Entries
    1

    Default

    Water pressure drops occur on modern houses regardless. On a new system, the unit should be backwashed a few times before you will get almost no restriction. I would push the regeneration button and release it, the system will regenerate tonight. New softeners should be regenerated a couple times prior to use to thoroughly clean the resin bed.

    A very common problem on larger houses is the use of small pex lines going long distances. A softner will add a very small amount of pressure drop, almost insignificant, but if the 1/2" pex tube is run too long already, that small amount of pressure drop may put the pipe over the edge. It is most common at the upstairs bathroom shower that is farthest away from the water inlet to the house.

    For fun, after the system regenerates, go into Diagnostics mode. You can see the current flow rate, peak flow rate, etc.

    Press the up and regeneration button simultaneously for 5-8 seconds,

    FR is the current flow rate. You should be able to get 15+ GPM through the system without any problem.

    The RR is not used to rinse salt off, the BR cycle does that. The BR stands for Brine and slow rinse. The system should remove the salt from the brine tank in about 10-20 minutes, then the remainder of the time is a slow rinse. In the 7000 service manual, or an earlier post you will see the flow rate of the slow rinse. The rapid rinse packs the bed down, and provides high quality soft water as soon as the regeneration is complete. In theory, a system does not really need a fast rinse, but it is worth the 10-15 gallons.

  15. #15
    DIY Member silversaver's Avatar
    Join Date
    Jan 2013
    Location
    Orange County, CA
    Posts
    42

    Default

    Great advise as usual, Dittohead. I do find the water unclear and plastic smell when the system first install... after few backwashes and regeneration, it is muh better now. You are right, the water flow rate has increase. (5 regenerations) I finally felt I made the right decision

    I have your cheat sheet setting now and since I have an 8 months old, would a higher salt setting making an smoother water?
    Last edited by silversaver; 01-25-2013 at 10:25 PM.

Similar Threads

  1. New fleck 7000 sxt questions
    By Steve424 in forum Water Softener Forum, problems, installation and reviews
    Replies: 14
    Last Post: 12-04-2012, 01:31 PM
  2. Fleck 7000 questions
    By cgarai in forum Water Softener Forum, problems, installation and reviews
    Replies: 9
    Last Post: 11-16-2012, 12:47 AM
  3. Problem with Fleck 7000 45k water softener
    By dergrah in forum Water Softener Forum, problems, installation and reviews
    Replies: 16
    Last Post: 08-08-2011, 06:34 PM
  4. Connecting a 1-1/4" fleck 7000 bypass valve to water supply
    By geod in forum Water Softener Forum, problems, installation and reviews
    Replies: 3
    Last Post: 03-01-2011, 10:34 AM
  5. Help Programming a Fleck 7000 SXT
    By batboy in forum Water Softener Forum, problems, installation and reviews
    Replies: 36
    Last Post: 09-03-2010, 06:43 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •