    Default hook up of table saw

    i have an existing just bought a new table saw/ 230 volt/ draws 13.4 amps. factory wire size is 14 ga. wire, seems small but is factory, saw came from cab. shop. would like to hook up to existing circuit which has a 30 amp. breaker with each leg reading 122 volts and has large 6 ga. wire. can i use existing wire possibly with smaller breaker or pull new wire which i really don't want to do? thanks

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Seems like you should be on a 20 amp breaker, max. It the 14 ga. you refer to is an appliance cord, that does not necessarily have to comply with the rules for permanent wiring. A larger gauge on that cord would be a good idea, and there is no problem feeding it with 6 ga, just use the correct breaker.

  3. #3
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    331

    Default

    Quote Originally Posted by rmuir View Post
    i have an existing just bought a new table saw/ 230 volt/ draws 13.4 amps. factory wire size is 14 ga. wire, seems small but is factory, .....
    That is not a problem.

    would like to hook up to existing circuit which has a 30 amp. breaker
    What is the horsepower rating of the motor? You may be ok.

    with each leg reading 122 volts
    Make sure you have 240V phase to phase.

    and has large 6 ga. wire. can i use existing wire possibly with smaller breaker or pull new wire which i really don't want to do? thanks
    You don't have to pull new wire. Whether you need to use a smaller breaker depends on the H.P. rating of the saw. Less than three horse and you would need a 20A breaker.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,685

    Default

    Your biggest prolem might be fitting a #6 wire into a 20 amp breaker's terminals. I am not even sure how they got it into a 30 amp breaker.
    Licensed residential and commercial plumber

  5. #5
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by hj View Post
    Your biggest prolem might be fitting a #6 wire into a 20 amp breaker's terminals. I am not even sure how they got it into a 30 amp breaker.
    Just pigtail it with #12.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,685

    Default

    If that was how they attached it to the existing 30 amp breaker, it makes using #6 a stupid idea in the first place.
    Licensed residential and commercial plumber

  7. #7
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    331

    Default

    Quote Originally Posted by hj View Post
    If that was how they attached it to the existing 30 amp breaker, it makes using #6 a stupid idea in the first place.
    Not really. Amps are equal in a circuit, unless there is a problem with it. Upsizing conductors to overcome voltage drop can be done anywhere along the circuit.

    Maybe whoever installed the circuit had enough #6 to get the job done, so there was no need to spend money on a new roll of wire.

    It could also be that the circuit was originally meant for another purpose but it never got used.

Similar Threads

  1. table saw question
    By shluffer in forum Remodel Forum & Blog
    Replies: 24
    Last Post: 05-23-2008, 07:58 AM
  2. Pump Table Question
    By MarkMcK in forum Pumps and Tanks Well Forum & Blog
    Replies: 2
    Last Post: 05-13-2008, 10:13 AM
  3. Table Lamp
    By Fudog in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 01-01-2008, 06:24 AM
  4. Mission Impossible: Table Saw
    By statjunk in forum Remodel Forum & Blog
    Replies: 6
    Last Post: 10-02-2007, 01:12 PM
  5. table or chart for AWG
    By hids2000 in forum Electrical Forum discussion & Blog
    Replies: 18
    Last Post: 08-14-2007, 03:57 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •