As part of a basement remodel I'm planning out the rough-in for adding a bath on slab, residential dwelling. I'm going to connect a lav drain line line to an existing below slab 2" PVC buried line. I'll be adding a 2" horizontal 'Y' to the existing line and I've heard PVC repair couplings are notorious for not getting a water tight weld. I'm checking with the city if I can use shielded couplings.

Alternatively, although I hate adding four 90 degree sweeps to a horizontal line, I could reroute the line to accomodate the new fitting as in the attached drawing? The existing 2" line services only a single bar sink.

thanks for any advice

TapIn.jpg
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
There's a limit on the total number of degrees you can turn a drain before a cleanout is required, and I think that would exceed it. WHy not just put a wye in the straight existing pipe? You do need to maintain the 1/4" per foot drop, and offsetting things might let you achieve that, but it shouldn't be a major deal most of the time.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
I would install a wye off the line, using mission couplings that are schedule 40 size. And no, they don't leak.
We use them all the time. Adding that many 90 bends is asking for trouble.

mission_bandseal.jpg
 