    Default Plumbing two new bathrooms one above the other and then to main stack?

    I am adding a half bath on the first floor and a 3/4 bath on the second. They are stacked above and below each other. It will be all new plumbing on the left side branch of my drawing. Do you see any problems with my venting of the two baths together using a 3" stack? What fittings are necessary for the connections on each floor?

    Horizontal distance from new stack (on the left) to main(original) CI stack where I will tie in is about 7feet. The new WC on the second floor will be about 3feet from the new stack so horizontal distance will be right around 10 feet total after all the drop.

    Long sweep at bottom of new stack with cleanout wye above?

    Sinks=1 1/2", shower 2" and "3 inch for stack and WC to the basement.


    Name:  two new bathrooms plumbing.jpg
Views: 1490
Size:  29.2 KB

  2. #2
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Any wet venting has to be on the same floor, a bathroom group in a residence.

    The toilet vent, or wet vent needs to happen before the waste from upstairs enters the line.
    So the downstairs lav would need to wye in closer to the downstairs toilet, "before" the wye for the upstairs bath.

    Also, the upstairs shower needs a vent between the it's trap arm and the stack below the toilet.
    The vent needs to come off the top of the trap arm, you can't go up after a vent, except for the normal 1/4" per foot grade, within five feet.

    Longer then that, not allowed
    More grade then that, not allowed.
    Last edited by Terry; 01-03-2013 at 12:41 PM.

  3. #3
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default First floor wet venting

    First floor wet venting of WC using sink (2") so that the venting is before the y. Vent connects above flood level on second floor. Correct?

    Does it need a vent where it finally turns vertical to tie in at the main stack in the basement? (Red hand pointing to the 90 elbow at the bottom of the drawing.)

    Name:  both levels.jpg
Views: 1506
Size:  36.0 KB
    Last edited by tireiron; 01-04-2013 at 09:29 PM. Reason: new drawing

  4. #4
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default Venting the shower upstairs

    See my options for venting the shower a couple posts below.
    Last edited by tireiron; 01-04-2013 at 09:35 PM.

  5. #5
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default

    Wondering if adding a vent for the WC before the wye that connects the lav is a good option?
    Last edited by tireiron; 01-04-2013 at 09:37 PM.

  6. #6
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default New questions and new drawing

    Going back to the original drawing to work things out. Thank you hj for steering me away from the albatross.
    Attached Images Attached Images  
    Last edited by tireiron; 01-04-2013 at 09:31 PM. Reason: sketches confused discussion

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    You started with a "simple" design which needed a few revisions and have created a "monster". The "second" drawing is completely wrong because you cannot connect the vent back below the upstairs bath. From you drawing it appears you are putting the pipes below the joists so you can use a side inlet "T" for the lav and shower inlet. This is NOT the place to give you a tutorial on installing drains and vents, but if it were I, I might throw your entire drawings away and start over with a much simpler design than any of them.
    Licensed residential and commercial plumber

  8. #8
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default

    I understand this is not a tutorial site. Too much time last night I guess. I was searching the forum for examples and found someone else's example that was "approved" and modified it by removing bath from first floor bath to match my intentions. Came up with all sorts of monsters.

    In the original drawing I was using a t for the horizontal lav to sink inlet. The shower drain is less than three feet from the new vent stack. I can run that by itself to a wye to connect it without combining them. The stack would qualify as the vent for the shower since it is so close.
    Last edited by tireiron; 01-04-2013 at 06:19 AM.

  9. #9
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    quote; The stack would qualify as the vent for the shower since it is so close.

    NOT NECESSARILY. That is like saying that milk will not spoil if it is on the table close to the refrigerator. IF the shower's Y is between the vent and the toilet, then the stack will NOT, nor can it, be the shower's vent.
    Licensed residential and commercial plumber

  10. #10
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default

    Quote Originally Posted by hj View Post
    quote; The stack would qualify as the vent for the shower since it is so close.

    NOT NECESSARILY. That is like saying that milk will not spoil if it is on the table close to the refrigerator. IF the shower's Y is between the vent and the toilet, then the stack will NOT, nor can it, be the shower's vent.
    Are you meaning that if the shower's Y is on the horizontal between the WC and the vent it would need its own vent?

    What I meant was I would go directly to the stack with its own sani-T rather than combine with the horizontal line from the WC/lav. Either stack two sani-T fittings vertically or use a sani-T hub (which I do not know if it is ok and asked about it in another thread). Name:  sanitary T_4871.jpg
Views: 706
Size:  6.8 KB

    It is mightily difficult to tie in the lav vent to the 3 inch stack in the attic but simpler just to have another roof penetration instead. How the shower branch connects and vents is what is left to figure out. Use sani-T hub, two vertical sani-T's or ? Without the shower the second floor plumbing looks like this so far. The shower is 90 degrees from the direction the WC comes in (hence the 3x3x3x2 hub thought).
    Name:  upper bath redrawn copy.jpg
Views: 1125
Size:  58.6 KB

  11. #11
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default Shower connection options?

    Options:
    1.Use a combo sani-T hub 3x3x3x2 (would simplify things). Stack acts as vent for the shower.
    2.Use a vented branch to a 3x3x2 sani-t. Venting required for the drop to get below the wc connecting sani-T.
    3. Connect shower to lav waste via a Y fitting and add 2" vent near connection to3" Y between WC and stack vent. (Tie into WC 2" vent or into stack on its own?)
    First Option:
    Name:  hub_shower connection.jpg
Views: 1369
Size:  69.6 KB
    Second Option:
    Name:  vented sani-T upper bath.jpg
Views: 844
Size:  64.8 KB
    Third Option:
    Name:  third option.jpg
Views: 760
Size:  60.9 KB
    Last edited by tireiron; 01-04-2013 at 09:32 PM. Reason: third option

  12. #12
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,633

    Default

    I don't know how much "flexbility" you have as far as the pipe installation goes, but if it could be done, I would install the 3" stack at the lavatory with the 3x3x3x2 tee below it. Run the shower into the side, "offset" the toilet to its required location, and use a 3x1 1/2" tee for the sink. The way you have it drawn, however, NONE of the installations need the 2" vent at the toilet. Third option, neither the 2" for the toilet, nor that "cosmetic" vent on the sink/shower drain is necessary. There could be other possible "easier" layouts, if we knew the floor plan and fixture locations, or if you have a great deal of latitude on where the fixtures will be located, which seems to be case according to your various drawings.
    Licensed residential and commercial plumber

  13. #13
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default Project photos for reference

    The projects are in the garage and the bonus room above the garage utilizing a dormer area for a shower. The proposed 3" stack location is firm. The space above the stack in the kneewall is 50 inches tall. I can route it up the rafters to exit above the dormer valley. It lines up with vertically with the proposed bathroom wall below and the route to the basement to tie into CI stack. Nothing is framed on either floor, hence some flexibility. The hole through the poured concrete foundation on the first floor has been cut to access the CI stack in the basement.

    Here are some pics for reference.

    Name:  Bath floor plan area.jpg
Views: 706
Size:  56.3 KBName:  second floor bath plan.jpg
Views: 694
Size:  55.3 KBAttachment 18499Name:  Bonus Room Floor Plan.jpg
Views: 698
Size:  42.0 KB
    Last edited by tireiron; 01-09-2013 at 07:44 AM.

  14. #14
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,201
    Blog Entries
    1

    Default

    Something like this works if you run 2" to the lav for the wet vent.
    A wet vent minimum size is 2" on the wet portion.

    The other drawing where you vent the shower by itself is good too.
    It looks like you are learning. These latest drawings are head and shoulder better than the first one.
    Attached Images Attached Images  
    Last edited by Terry; 01-05-2013 at 11:31 AM.

  15. #15
    DIY Junior Member tireiron's Avatar
    Join Date
    Jan 2013
    Location
    MN
    Posts
    18

    Default

    Thanks for pointing out the increase to 2" vent from the lav for the wet vent. As indicated by hj I would simplify the design and remove the 2" for the toilet and the "cosmetic" vent on the sink/shower drain, also.

    Does the venting on the first floor look good?

Similar Threads

  1. Main stack
    By novicepiper in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 03-15-2011, 12:17 PM
  2. Plumbing bathrooms and kitchen, UPC
    By Mike58 in forum UPC Plumbing Code Questions
    Replies: 2
    Last Post: 06-10-2010, 06:54 AM
  3. Plumbing bathrooms and kitchen, UPC
    By Mike58 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 06-10-2010, 06:54 AM
  4. Drywall / ceiling choice for stacked bathrooms with plumbing in between
    By Scott99999 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 11-15-2009, 07:48 PM
  5. main stack jog?
    By pipewoe in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 05-10-2007, 02:49 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •