Thread: Convert from zone valve to zone pumps

  1. #1
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default Convert from zone valve to zone pumps

    Right now I have a 1 punp 3 zone hydro. One HW and 2 living. I want to add a radient underfloor loop via mixing valve. While doing this it seems cleaner to just do all the zones with new pumps and a 4 zone switch relay. I have the pumps already so the cost to convert is not an issue. The question I have is:

    do the pumps for each zone act as valves. What I mean is... If a zone is not active and another is.... Is anything needed to isolate the zone as a zone valve does? Or will the pumps do this? (i.e. when pump is not moving it is a closed zone) All the schemas I have seen show the boiler --> pump --> zone --> boiler.

    This is a nice little spring project I have planned.

    Curently I have one zone running way too many radiators. 2 floors on zone, small room on zone 2, HW on zone 3.

    I want to clean this up and have living spaces on 1, bedrooms on 2, Basement on 3, HW on 4.

  2. #2
    In the trades Dana's Avatar
    Join Date
    Jan 2009
    Location
    01609
    Posts
    2,730

    Default

    You'll need a check valve in series with each pump, since the pressure differences created any one pump driving from the manifold will induce a reverse flow on the others. On very high head loops that may never present a practical issue, but on shorter hydronic loops that back flow can create unintentional heating of the "off" zones.

    When reconfiguring, try to avoid micro-zones, since that causes short-cycling efficiency losses and unnecessary wear & tear on the boiler. If your current smaller zone 2 has just a low-mass stick of fin-tube for a heat emitter, it's almost certainly short-cycling on that zone. Zoning it by floors is usually pretty reasonable, as long as the room-to-room balance has been properly dealt with by load-proportional room-to-room radiation sizing (based on the room-by-room heat loads, not the square footage of the space.)

  3. #3
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    I understand. The Taco pumps I have have the check built in. IFC. so that should cover that.

    TY for your reply it was dead on what I was looking for.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,687

    Default

    I question whether a "4 zone switching relay" will do what you want it to, because that usually controls ONE pump and four low voltage zone valves. For your system, you will probably need four thermostats and four pump control relays, and EACH of them would need the contacts, in parallel, to operate the boiler's burner.
    Licensed residential and commercial plumber

  5. #5
    DIY Senior Member rockycmt's Avatar
    Join Date
    Nov 2007
    Location
    New York
    Posts
    129

    Default

    Quote Originally Posted by hj View Post
    I question whether a "4 zone switching relay" will do what you want it to, because that usually controls ONE pump and four low voltage zone valves. For your system, you will probably need four thermostats and four pump control relays, and EACH of them would need the contacts, in parallel, to operate the boiler's burner.
    I disagree. This is exactly what I will use.
    http://www.pexsupply.com/Taco-SR504-...witching-Relay

Similar Threads

  1. Weil-McLain GV90+3 - Are zone circulator pumps needed?
    By jay19144 in forum Boiler Forum
    Replies: 1
    Last Post: 10-20-2012, 09:52 AM
  2. 2 zone system-no heat upstairs-Boiler doesn't fire when that zone asks for heat
    By MrBostn in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 14
    Last Post: 10-13-2012, 08:33 AM
  3. Boiler not firing up for 2nd zone, only 1st zone
    By bjferri in forum HVAC Heating & Cooling
    Replies: 4
    Last Post: 11-04-2009, 03:50 PM
  4. Well guy...made my 4 zone sprinkler sys, now a 2 zone???
    By iPhoneSRQ in forum Pumps and Tanks Well Forum & Blog
    Replies: 10
    Last Post: 04-21-2009, 07:58 AM
  5. Dual zone vs. Single zone?
    By zombieman in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 03-04-2009, 04:48 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •