    Basement toilet and shower rough-in is in the planning stage. Is there a chance that the horizontal section of the vent could clog in this arrangement. Nothing is finalized yet.
    Attached Images Attached Images  
    Last edited by rosem637; 01-01-2013 at 09:06 AM.

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,134

    Default

    That would not be an approved install anywhere in the U.S. that I am aware of.

    All vent take-offs must rise vertically to a level at least 42" above the floor.

  3. #3
    DIY Member rosem637's Avatar
    Join Date
    Jan 2013
    Location
    Michigan
    Posts
    38

    Default

    How about this? Fittings 3 and 7 are rolled a little bit off the horizomtal.
    Attached Images Attached Images  

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,134

    Default

    You are wasting your efforts.

    The angle of any section of vent below 42" must be greater than 45 degrees.

    You are going to need to re-think your drain and vent routing.

    What is that pipe coming down from above? If is is a drain for any fixture on the upper levels, you cannot make a vent connection to it in the basement.

    A shower's vent can be 1-1/2", but the drain should be 2".
    Last edited by cacher_chick; 01-01-2013 at 01:21 PM.

  5. #5
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    I can see why you'd rather not, but you're going to need to move the double wye downstream, so the vents can rise vertically inside that stud wall there.

    I know it means breaking more concrete, and distrupting your laundry room area, but it's the proper way.

    You just CANNOT have horizontal vent piping under the floor.

  6. #6
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,933

    Default

    Neither vent is allowed.
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  7. #7
    DIY Member rosem637's Avatar
    Join Date
    Jan 2013
    Location
    Michigan
    Posts
    38

    Default

    Quote Originally Posted by dlarrivee View Post
    I can see why you'd rather not, but you're going to need to move the double wye downstream, so the vents can rise vertically inside that stud wall there.
    I know it means breaking more concrete, and distrupting your laundry room area, but it's the proper way.
    Thats what I was afraid of.

    Quote Originally Posted by cacher_chick View Post
    You are wasting your efforts.
    Not wasting anything as I am trying to determine the correct way.

    Quote Originally Posted by cacher_chick View Post
    What is that pipe coming down from above? If is is a drain for any fixture on the upper levels, you cannot make a vent connection to it in the basement.
    There use to be a basement laundry sink on the other side so that stack rising is all venting. Thanks

Similar Threads

  1. Basement Bath Shower Pan Planning
    By duggerce in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 01-30-2010, 10:14 PM
  2. Planning a basement bathroom from scratch
    By DVMSteve in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 12-05-2009, 09:57 PM
  3. Basement bathroom planning
    By ktambascio in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 05-16-2009, 08:03 PM
  4. Basement toilet rough-in
    By kencarlow in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 1
    Last Post: 11-10-2008, 03:07 PM
  5. Basement Rough-In & DWV Planning Advice
    By TonyT in forum Toilet Forum discussions
    Replies: 1
    Last Post: 03-31-2005, 08:28 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •