Overload trips about once a week.

Users who are viewing this thread

Rocklin662

New Member
Messages
15
Reaction score
1
Points
3
Location
Roseville, CA
In the past three weeks the overload on the bottom left of the motor control has tripped while someone was taking a shower. It is a 2hp submersible pump on 2" ? pipe in a 6" well casing. About 2 feet of the casing are sticking out of the ground and the pump control box is mounted on top of the casing. The well was drilled in 1979 and from the documents the depth was 210', the static water level was 115' and the 4 hour flow was 30 gpm. The control box is a Franklin Electric 2823018110. I downloaded the manual from Franklin Electric and will run through the tests on Tuesday. The control box is mounted in direct sun and the manual cautions against that. It does get fairly hot here on the edge of Sacramento.
 

Valveman

Cary Austin
Staff member
Messages
14,599
Reaction score
1,296
Points
113
Location
Lubbock, Texas
Website
cyclestopvalves.com
Tripping an overload while taking a shower usually means the motor is tripping out from cycling on and off. It could just be a weak start cap or relay, but I am guessing you should be prepared to replace the pump/motor.
 

Rocklin662

New Member
Messages
15
Reaction score
1
Points
3
Location
Roseville, CA
Did a bit of testing today. Using Min/Max on Fluke 87 meter reading as follows. Line voltage dropped from 241.4 VAC to 234 VAC when the pump turned on. I would have expected the current on the red (start) conductor to go higher. Both capacitors appear to be open. The run capacitor is in a rusty metal case but the start capacitor appears to be newer. Coil tests ok.
Measured:
Color Start Run
Red 4.0A 3.3A
Yellow 44.8A 12.8A
Black 44.0A 11.8A

From Table:
Color Full Load Maximum Load
Red 2.6A 2.6A
Yellow 10A 13.2A
Black 9.3A 11.9A
 
Last edited:

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I would replace the caps or at least check them.

Your readings are a little confusing, or maybe they are wrong.
 
Top