    Default Water Heater Installation

    My plan (up until now?) was to use 1" line for both hot and cold to feed entire house (new construction).
    I just bought a water heater and notice that it is 3/4" both in and out.
    Would I gain anything by going in with the 3/4" but, immediately coming out on hot side, adapting up to 1" to feed all hot water faucets of house?

    Thank you,
    Paul

  2. #2
    In the Trades Gary Swart's Avatar
    Join Date
    Sep 2004
    Location
    Yakima WA
    Posts
    7,246

    Default

    Actually you will lose by increasing the size of the pipe coming out of the heater and going to the rest of the house. The hot water in the pipes will cool when water is not flowing through them. Before you get hot water to the fixture, all of that cooled water will have to be purged (wasted) before you will have hot water. What many of us do is to use a recirculating system which will provide virtually instant hot water at any fixture. Also, 1" is far too large for a house distribution system. Depending on the number of fixtures involved, 3/4" might even be larger than necessary. There are tables that will provide optimum pipe sizes. You should investigate a recirculating system before completing construction as the better ones require a return line...that's what makes the recirculation possible. There are several very good brands available and the cost is not too bad. Many have timers on the pump so they only recirculate at the set times. I have one that does not use a timer that has been in service 24/7 for several years without a problem. If/when the pump fails, it is located where it can be easily replaced. Keep a watch on this thread, someone will likely provide the sizing information in better detail.

  3. #3
    DIY Junior Member abc's Avatar
    Join Date
    Nov 2012
    Location
    Mexico
    Posts
    8

    Default

    Thank you Gary
    I researched pipe sizes on the internet and was surprised to see that, for any normal household fixtures, 1/2" pipe throughout house is sufficient.
    This may be true for a city-supplied water system of high pressure, but as in all houses down here, we use gravity-fed systems (please don't suggest adding pump). Would this 1/2" pipe size still be adequate for a lower pressure gravity-fed system?
    Paul

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,632

    Default

    I haave nEVER considered 1/2" pipe of any kind adequate for use "throughout the house". What KIND of pipe are you using. I assume it is plastic CPVC or PEX. If so if you use 1" tubing it will be almost the same as if you used 3/4" copper and 1/2" would be completely inadequate.
    Licensed residential and commercial plumber

Similar Threads

  1. Electric Water Heater installation questions
    By JerryR in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 0
    Last Post: 01-12-2012, 07:11 PM
  2. Water Heater prices and installation
    By dachd in forum Water Heater Forum, Tanks
    Replies: 4
    Last Post: 01-15-2011, 10:33 PM
  3. water heater installation
    By billhayton in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 12
    Last Post: 12-17-2007, 07:38 AM
  4. Does a dual water heater installation require that the water heaters be the same size
    By GooSkinBaldi in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 4
    Last Post: 04-29-2007, 02:28 PM
  5. Tankless Water Heater Installation Cost?
    By rdtompki in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 10
    Last Post: 03-22-2006, 11:13 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •