3/4 to 1/2 valve/pipe for shower head

Users who are viewing this thread

tomdiy

New Member
Messages
2
Reaction score
0
Points
0
Location
nj
Shower installation with two shower heads each on its own volume valve. The supply into the kohler themostatic valve is 3/4 pex into 3/4 cooper into the valve, exiting the valve is 3/4 copper reduced to 1/2 copper then into each of the 1/2 volume valve and 1/2 copper out to the shower heads, both shower heads seem light on flow both hot and cold (Other fixtures on same feed are fine), Kohler says I should have keep it all 3/4 after the valve but don't most shower heads have to reduce to 1/2 at some point? I was going to replace the valve cartridge to see if it helped but figured I would ask for thoughts before spending the money. Thanks in advance
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Unless you removed the restrictor (some can be easily, some can't), each shower head is mandated to have a max of 2.5gpm. But, 1/2" pex might be hard pressed to provide 5gpm. The ID of pex is considerably smaller than that of copper in the same 'size' (which is the OD, not the ID). This is because copper is much stronger, so it can be thinner than pex. What's strange to some is that 1/2" copper is unlikely to be 1/2" ID and it is 5/8" OD, although it is much closer to 1/2" than pex.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; What's strange to some is that 1/2" copper is unlikely to be 1/2" ID and it is 5/8" OD

The i.d. is determined by the tubing's wall thickness. Type "K" with the thickest wall is ALMOST 1/2" i.d., about 1/40" larger than actual 1/2".
 

tomdiy

New Member
Messages
2
Reaction score
0
Points
0
Location
nj
Thanks, I guess I was not clear, the flow I am getting is less than I have from predominately 1/2 inch in the other bathrooms, why would 3/4 supply reduced to 1/2 for the last 10 feet of the run after a valve reduce the flow to less than a run which is mostly 1/2 inch
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Few valves' internal passages are the same diameter as the supply pipes. IF the pipe supplying and outlet of the valve are both the same size, the flow rate increases in the valve and it doesn't act like a restrictor much (the venture effect). If the outlet pipe is smaller, it stays slowed down and the valve is a real restriction to flow. The outlet of a faucet goes through the spout, which is usually unrestricted (well, it may have an aerator on it).
 