    Default Derating Confusion

    9CC being the max, is the CC only the Hot or also the Neutral when taking this into equation.

    I've got 8-9 Hots of 12AWG, and a pair of #10 (G and N) going from a transfer switch back to a panel.
    AND Then, I just came across this derating issue...

    So to be complaint, it looks like instead of the 1" I was planning to run, I should run two 3/4 Back to the Panel and then split the lines from the transfer going back via 2 conduits.
    Last edited by chefwong; 12-19-2012 at 03:38 AM.

  2. #2
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    326

    Default

    By pairs do you mean one hot and one neutral?

  3. #3
    DIY Senior Member chefwong's Avatar
    Join Date
    Jun 2006
    Location
    District of Columbia
    Posts
    710

    Default

    Corrected my OP. The length of pipe between the transfer switch and panel is around 42" - 4 feet.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    What makes you think ONE #10 neutral, the ground size is somewhat immaterial, will be sufficient for 8 or 9 #12 "hot" feeds, in the first place?
    Licensed residential and commercial plumber

  5. #5
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    You must count all of the current carrying conductors.

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    You would derate all conductor to 70% which would mean that you would need a #2 neutral

    Just what kind of generator are you connecting to your home?

  7. #7
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default

    quote; which would mean that you would need a #2 neutral

    Good luck twisting that under the terminal of a duplex receptacle.
    Licensed residential and commercial plumber

  8. #8
    DIY Senior Member BobL43's Avatar
    Join Date
    Mar 2011
    Location
    Long Island, NY
    Posts
    1,768

    Default

    Quote Originally Posted by hj View Post
    quote; which would mean that you would need a #2 neutral

    Good luck twisting that under the terminal of a duplex receptacle.
    just clip off the excess strands lol, NOT
    I am definitely not a pro plumber, but I am a pro crastinator

  9. #9
    DIY Junior Member kenwalkerconst's Avatar
    Join Date
    Dec 2012
    Location
    Pinson, Al ( Birmingham )
    Posts
    9

    Default

    I'm not sure I'm understanding the question in the first place but the two line legs of 110V carry the current and have a canceling effect with the neutral carrying the imbalance. Think about you service entrance cable, TWO line legs with ONE neutral. Theoretically if you could balance both line legs you would not need the neutral. That what causes wierd things to happen when you "loose the neutral". Large 110V items on one leg like a refigerator comes on and light bulbs blow that are connected to the other leg. The refigerator drags down the voltage to say 50V on one line leg causing the other leg to see the imbalance of ( 220V less 50V = ) 170V.

  10. #10
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,140

    Default

    He was asking about derating the conductors because they are being run in conduit.

Similar Threads

  1. Derating large conductors in attic?
    By Homeownerinburb in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 07-29-2012, 10:41 PM
  2. Please check my derating calculations.
    By rick15752 in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 01-20-2011, 05:16 AM
  3. Derating bundled wires on same circuit
    By rerickson in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 05-22-2010, 12:13 PM
  4. Derating for number of conductors in conduit
    By cacher_chick in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 02-22-2010, 07:49 PM
  5. bit of confusion now...
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 11
    Last Post: 03-21-2008, 12:46 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •