    Default Low flow at radiant manifold

    I just installed a pex radiant heating system in between the joists in my subfloor and I'm having trouble getting sufficient flow at the supply manifold. I have 4, 250ft loops connected to manifolds which are centrally located in my house.

    Here is a picture of the 4-port supply manifold assembly I'm using:


    It has 4 ports on the supply and return manifold. The supply manifold has an adjustable flow meter, and the return has a balancer. This is to allow you to adjust the flow so that it is equal in each of the four loops.

    My furnace has a 3/4" copper supply line. I've reduced this to 1/2" PEX and ran that to the hot side of a 1" mixing valve. (There is a 1/2" x 1" reducer bushing installed on the mixing valve to accept the 1/2" pex)

    The outlet of the mixing valve is then reduced from 1" to 1/2" pex, which is then connected to the 1" supply fitting on my supply manifold. (with another 1/2" x 1" reducer bushing)

    My supply manifold has flow meters on each of the 4 loops, and I cannot get flow above 0.2gpm out of each of these lines. I need the flow to be around 2gpm.

    Do you think this is because of the size of my pex lines? I'm thinking I should purchase 3/4" PEX and run that instead of 1/2" pex, but I do not want to spend the money on these fittings if it is not going to fix my problem. I'm also going to need to buy 100ft of 3/4" pex, when I only need to use about 20ft.

    FYI: From everything I've read online, 90% of the time flow problems are because of air trapped in the loops. I spent about an hour and a half yesterday trying to purge the air from the lines, but my flow is so low that I do not think this is possible. What I've been instructed to do is shut the main valve on the return manifold and connect a garden hose to the drain valve on the the return manifold. Then I flow water through 1 loop at a time for 15 minutes out the garden hose to remove the air. When I do this the water is flowing out the hose very slowly...not the steady stream that I'd expect.

    Attached is a basic diagram showing my plumbing layout...minus all the little fittings that I described above.


    If you have any questions let me know and thanks in advance for your help.

  2. #2
    In the Trades Tom Sawyer's Avatar
    Join Date
    Nov 2010
    Location
    Maine
    Posts
    2,940

    Default

    The circulator should be on the supply.
    The feed piping to the manifolds should be 3/4"
    There should be a circulator to feed the manifold
    The primary/secondary tee's should be no further than 4" from each other.
    In other words, it all needs to be re-piped. Water always follows the path of least resistance
    [B]No, plumbing ain't rocket science. Unlike rocket science, plumbing requires a license[B]

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default

    Your mixer and manifolds are BOTH 1", so why in the world would you reduce them to 1/2" PEX, which is really about the same a 3/8" i.d. copper? (1" PEX would be just about the same size as your 3/4" copper to the expansion tank connection). Your piping is NOT big enough to support 1000' of radiant tubing. Those valves on the manifold inlets are NOT helping to maintain maximum flow either.
    Licensed residential and commercial plumber

Similar Threads

  1. Water Pressure Issues - WEAK Flow Then VERY Strong Flow.
    By 3baysofplay in forum Pumps and Tanks Well Forum & Blog
    Replies: 18
    Last Post: 08-09-2012, 04:50 AM
  2. How to increase low flow toilets water flow
    By Lisa J. in forum Toilet Forum discussions
    Replies: 16
    Last Post: 07-26-2011, 01:31 PM
  3. Shower head flow restrictor blocks all flow??
    By K. in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 09-07-2010, 09:25 PM
  4. Restricted flow in radiant floor
    By Repair Man Rex in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 3
    Last Post: 02-01-2010, 05:02 PM
  5. Flow rate? Flow thru? Water softner restrictions.
    By polocash in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 2
    Last Post: 03-29-2005, 10:16 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •