I'm adding a half-bath to on the first floor and tying into an existing sanitary line for the full bath above. Below are two designs. Design "A" runs the vent for the half-bath above the flood level of the fixtures in the full bath. Design "B" is a bit simpler on paper, but the existing riser is in an exterior wall next to a post at the point of the tie-in, so its a bit trickier to build than design "A". The sketches don't show the jogs in plan-view, which some lengths I relate may look out of scale.

I annotated the sketches with ABS pipe sizes and lengths. Blue lines are the existing sanitary, green is the new.

Are both of these designs OK? Code-wise, I'm in Nova Scotia.

WashroomA.jpg
WashroomB.jpg
 

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Desigh "A" is the only one that will work and that assumes you actually install it the way it is drawn. "B" would not pass any code that I am aware of.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
"B" is not acceptable because once the line has been used for a drain, it can no longer be used as a vent. The only exception is the wet vent of the water closet past the lavatory.
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
"B" is the old "single stack" plumbing system design, as far as I know it was outlawed in the early part of the last century.
Also, in "A", I think you need to keep the toilet/lav vent size at 2 inches all the way up, rather than reducing down to 1 1/2
inch as shown.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,458
Points
113
Location
Bothell, Washington
Website
terrylove.com
A

And like mentioned above, keep the lav, including the vent, 2" all the way up to the next floor on the revent.
You can use the 1.5" traparm for the p-trap on the lav.

Below is an example of wet venting

dwv_b1.jpg
 
Last edited:

Buttonsrtoys

New Member
Messages
24
Reaction score
0
Points
1
Location
Nova Scotia, Canada
quote; Wet venting makes my head spin

Wet venting is simple, but your ""B" is an illegal "wet vent" because you cannot wet vent between floors.

Ah. That clarifies what was confusing me. So wet vents are OK provided their short/restricted to the same floor. Thanks! Now I'm curious - why are long wet vents between floors a problem?
 