    I'm adding a half-bath to on the first floor and tying into an existing sanitary line for the full bath above. Below are two designs. Design "A" runs the vent for the half-bath above the flood level of the fixtures in the full bath. Design "B" is a bit simpler on paper, but the existing riser is in an exterior wall next to a post at the point of the tie-in, so its a bit trickier to build than design "A". The sketches don't show the jogs in plan-view, which some lengths I relate may look out of scale.

    I annotated the sketches with ABS pipe sizes and lengths. Blue lines are the existing sanitary, green is the new.

    Are both of these designs OK? Code-wise, I'm in Nova Scotia.

    Name:  WashroomA.jpg
Views: 135
Size:  46.8 KB
    Name:  WashroomB.jpg
Views: 129
Size:  46.3 KB

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    Desigh "A" is the only one that will work and that assumes you actually install it the way it is drawn. "B" would not pass any code that I am aware of.
    Licensed residential and commercial plumber

  3. #3
    DIY Junior Member Buttonsrtoys's Avatar
    Join Date
    Nov 2012
    Location
    Nova Scotia, Canada
    Posts
    22

    Default

    Quote Originally Posted by hj View Post
    Desigh "A" is the only one that will work and that assumes you actually install it the way it is drawn. "B" would not pass any code that I am aware of.
    Thanks hj. I'll install "A" as drawn. What's wrong with "B"?

  4. #4
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,150

    Default

    "B" is not acceptable because once the line has been used for a drain, it can no longer be used as a vent. The only exception is the wet vent of the water closet past the lavatory.

  5. #5
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    "B" is the old "single stack" plumbing system design, as far as I know it was outlawed in the early part of the last century.
    Also, in "A", I think you need to keep the toilet/lav vent size at 2 inches all the way up, rather than reducing down to 1 1/2
    inch as shown.

  6. #6
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    A

    And like mentioned above, keep the lav, including the vent, 2" all the way up to the next floor on the revent.
    You can use the 1.5" traparm for the p-trap on the lav.

    Below is an example of wet venting

    Last edited by Terry; 12-16-2012 at 07:49 PM.

  7. #7
    DIY Junior Member Buttonsrtoys's Avatar
    Join Date
    Nov 2012
    Location
    Nova Scotia, Canada
    Posts
    22

    Default

    Thanks guys. "A" it is with a 2" vent. Wet venting makes my head spin...

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,653

    Default

    quote; Wet venting makes my head spin

    Wet venting is simple, but your ""B" is an illegal "wet vent" because you cannot wet vent between floors.
    Licensed residential and commercial plumber

  9. #9
    DIY Junior Member Buttonsrtoys's Avatar
    Join Date
    Nov 2012
    Location
    Nova Scotia, Canada
    Posts
    22

    Default

    Quote Originally Posted by hj View Post
    quote; Wet venting makes my head spin

    Wet venting is simple, but your ""B" is an illegal "wet vent" because you cannot wet vent between floors.
    Ah. That clarifies what was confusing me. So wet vents are OK provided their short/restricted to the same floor. Thanks! Now I'm curious - why are long wet vents between floors a problem?

  10. #10
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,202
    Blog Entries
    1

    Default

    why are long wet vents between floors a problem?
    The same reason that standpipes can only be so long. They siphon traps.

Similar Threads

  1. Toto Seat Designs
    By AdamSmith1800 in forum Toilet Forum discussions
    Replies: 17
    Last Post: 09-03-2013, 01:57 PM
  2. opinions on bath tub and basin stopper designs?
    By tom12 in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 10-14-2012, 07:07 AM
  3. bathroom and washroom remodel
    By brklynfrnt in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 6
    Last Post: 12-09-2009, 06:14 AM
  4. New washroom
    By chochitoca in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 07-17-2009, 04:35 PM
  5. Nibco Stem for washroom tub
    By jechow in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 12-05-2008, 08:20 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •