    Lip at linear drain.

    This lip is located about 6-8" from the shower's bathroom entry door. To prevent water from sneaking along the edge the drain was installed before the wall tile and brought right to the back wall. Then the tile notched into the drain base. The Schluter profile is set higher than the drain and works well at blocking water from sneaking out. The linear strainer works well bring the water flow into the drain. Other drain styles can offer up a little room for water to skirt over them.


    Bit of a trench drain version of a linear drain?

    Looks like this is an infinity drain. Did you have to modify the top grate's length to accommodate the wall tile entrance into the end of the drain channel? Otherwise I guess you could just install a shorter drain and angle the end tiles as you would any other mid-floor linear drain.

  2. #17
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default Only option is a curb

    John,

    Looking at my situation, 5/8" flooring and 1" of clearance from their to the threshold of the bathroom leaves me at most 1 5/8" from top of floor to threshold if I lower the flooring in the shower area to be flush with the top of the joists below. And maybe, just maybe I could squeeze and additional 1/4 to 1/2" depending if I try to lower the floor even more between the joist right where the drain is; in essence a step down from bathroom floor to shower floor and then to drain level floor.

    Looking at various linear and non linear drains, it seems you need pretty close to those dimensions just to get to the top of the installed drain. Correct?

    This for certain would then mean a curb on the non-door side of the shower, or the side glass would be 3/4" shorter at the back wall of the 3' deep shower which I'm not so sure will look all that great and then the glass wall then functions as the curb.

    Assuming I put the drain at the door without curb at the door , then I'll have to also deal with some additional means to help prevent water overshoots of the drain and water that runs down the door from going to far into the rest of the bathroom. All these measures, and thanks again for some suggestions and ideas on that, would mean an additonal height requirement above the drain be that a 1/8" rise of tile above top of drain at drain plus some slope on door side of the drain (be that just inside the shower or outside the shower). Based on previously mentioned 5/8" max water height above drain even when not blocked, that could mean some wet area outside the door for at least 2' (at 1/2" / ft slope, more at 1/4"). Could lead to having water reaching out from the shower to almost the toilet and that would not be good.

    Don't see how the use of a linear drain will work properly given my height restrictions without using a curb at the door. Have I missed something here or is there a product that could work within these constraints?

  3. #18
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,978
    Blog Entries
    5

    Default

    post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-17-2014 at 05:24 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  4. #19
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,978
    Blog Entries
    5

    Default

    post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-17-2014 at 05:24 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  5. #20
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    Thanks John. Lots to think about. I'd appreciate any pictures you could provide from your buddies place.

    Yes, deflection, support, slope, etc., all familiar to me as my real job was as a mechanical engineer for 20+ years. I've redone my deck that has now been solidly standing for 15 years, finished off my entire basement including some major plumbing changes below the concrete basement floor, completely reno'd our kitchen last year, and many other projects. All look very professional. I hire pro's when I need to for certain inspection approvals, for speed in a tight timeline, or when I think it is a bit over my head or something I've not done before that I think has a long learning curve. I'm basically at the design stage and gaining information to see if I can do it and also if I can't I have enough knowledge to ensure the work of the pro's is done correctly or at least to be able to ask a few intelligent questions.

    For me, Electrical I just don't touch if it means running new wires, etc.. It has to be inspected, I'm not as aware of the codes for it that seem to change all the time so I always hire an electrician for that part. More efficient for me to do it that way. Most of the plumbing changes I do myself as my background was in water filtration equipment design and manufacture. Depending of the project I sometimes hire a plumber. For the rest I've taught myself and had no problems passing inpsections for framing, insulation/ vapour barrier, final approvals. I've done drywall (small jobs only, I'm no expert here but getting better), flooring, trim work, etc.. So I know my capabilities and when the work is above them.

    Haven't done much tiling except for a backsplash with rather large tiles in the kitchen so that may be something that a pro could do for me in a couple of days and I do have a friend that does that for a living so a few pizzas and some cold ones and long weekend and it could get done but I'll decide that later on.

    My first concern is to get the plumbing and electrical changes done so that I can close off the floor, walls and ceiling.

  6. #21
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    FWIW, since I put pex hydronic heat in my bathroom embedded in slc, the bathroom floor is quite a bit higher than the rooms outside. I had my granite fabricator make me some custom thresholds with a taper (set like a big tile at the entry) to make the entry acceptable. There are pre-made ramps available if you have carpeting outside the bathroom that will take up the difference, but if wood, then custom milling is probably the best way to go.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #22
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    Actually the bathroom floor is off the master bedroom which currently has carpets but...as soon as the bathroom is done I will be ripping up the bedroom carpet so I have options. Hallway has carpeting at 3/4" or a slight bit higher so would be perfect match for hardwood in the bedroom or new carpeting. At 1" height in the bathroom, that is what was there, no need for a ramp of any type; it'll just be a slight 1/4" lip which is there now and is not a problem at all. This is what I'm aiming for right now. If I have to have a slight ramp at the entrance to bathroom for the ability to have a curbless entry to the shower then that's a tradeoff I'll have to decide that if it is worth it or not...depending on how high the ramp has to be.

  8. #23
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    Haven't looked at deflection at all yet for the majority of the bathroom as nothing is really changing yet drastically. Current joists are 2 x 10, 12' span, 24" OC.

    Only changes in bathroom are that a Victoria and Albert IOS tub will replace a jacuzzi tub that we had. So max 250 lbs of additional water there. New tub is about 100 lbs heavier than old tub but old tub also had pump and motor and full framing built around the tub so I'd call that even.

    Old shower is removed and replaced with new shower. Except for added weight on mud bed, if I go that way, don't see really any change there in total weight.

  9. #24
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Your deflection could be marginal for ceramic and is definately unsuitable for natural stone tile. It depends on the species of wood the joists are made of - if it is southern yellow pin or douglas fir, you're just above the minimums. If it is some other species, you should not tile it without beefing things up. This assumes that the joists are in good shape, not a lot of knots, no notches for plumbing or wiring, and to code holes for wiring and plumbing. Since your installation is marginal, anything not to code could put your joists below the minimum for a reliable tiled floor.

    24"oc means that between joist deflection is a problem, too. You'd want some significant subflooring to ensure that deflection is in spec as well.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #25
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    Sorry Jim,
    Saw 2 lines of screws on the floor and measured 24". Never occurred to me that it would be 12". They are actually 12" apart. What was ripped up was marble composite tiles that had been on the floor since 1989. No cracks or any problems in that time and this bathroom is used every day. The tile also had a 1/2" sublfoor on top of the 5/8" OSB.

  11. #26
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    12"oc verses 24"oc bumps the deflection to L/744 from L/372 or so...a BIG difference. Natural stone should be above L/720, and yours does if the species is SYP or DF and in good condition. It could still be marginal for natural stone if it is some other wood species.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  12. #27
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    The wood is in great condition from what I can see. House was brand new in 1989 and I see no signs of warping or excessive holes, etc.. There's been no changes to the house in this area since we moved in and we are the original owners. Wood is kiln-dried SPF (spruce pine fir). So should be fine. These are pretty good houses in a nice neighbourhood and most of the city is built by this home builder. From what I've seen in all my projects in this house, everything was built properly. I've seen no shortcuts or lazy workers remnants yet.

    But it is good to know that I can put down some natural stone if I want.

    thanks,

  13. #28
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,978
    Blog Entries
    5

    Default

    post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-17-2014 at 05:24 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

  14. #29
    DIY Member Freddie's Avatar
    Join Date
    Dec 2012
    Location
    Ottawa
    Posts
    54

    Default

    Hi John,

    Did a bit more research on ACO linear drains at exit and found the flowrate specs for the various drains and heads of water. Looks like minimum of 6 gpm on 36" shower drain with no head and around 8.5 gpm with 0.2" of head. So I would think with only 2 shower heads at 2.5 gpm there should be no problem especially if you lower the linear drain a bit below the tile level as you mentioned previously and then maybe a bit of dry side slope. I will probably try to fit in a wider shower stall, even if it is a few inches more say to fit in the roughly 40" drain. That'll also give me an additional 10% of flow capacity.

    Have you had any better success with any specific grate design in applications like this? They all seem to look good and I do like the lit drain option if it's not too expensive an option.

  15. #30
    ACO Shower Drain Sales johnfrwhipple's Avatar
    Join Date
    Jul 2009
    Location
    North Vancouver, BC
    Posts
    2,978
    Blog Entries
    5

    Default

    post(s) deleted by John Whipple
    Last edited by johnfrwhipple; 03-17-2014 at 05:25 AM.


    jfrwhipple@gmail.com - www-no-curb.com - 604 506 6792

    Always get construction advice double checked by your local city hall. Flood Test Every Shower - Every Time.

Similar Threads

  1. curbless shower
    By tucker2 in forum Shower & bathtub Forum & Blog
    Replies: 61
    Last Post: 02-10-2014, 02:04 AM
  2. ADA Curbless Showers in a Residence
    By PA Tile Guy in forum UPC Plumbing Code Questions
    Replies: 1
    Last Post: 07-18-2011, 05:01 PM
  3. Building 2 curbless doorless showers, need advice
    By crayola32 in forum Shower & bathtub Forum & Blog
    Replies: 8
    Last Post: 06-26-2011, 06:26 PM
  4. bath remodel curbless shower layout
    By grymes56 in forum Shower & bathtub Forum & Blog
    Replies: 2
    Last Post: 02-08-2010, 07:14 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •