    O.K I just got done building a wood boiler/ furnace for my garage and I have a couple questions. First one is, I made My own heat exchanger with a fan mounted behind it. What is the switch called that mounts to the copper pipe that turns the fan on when it senses heat in the pipe? Second can I use this HONEYWELL HEAT ONLY THERMOSTAT MODEL CT410B to turn on the circulator pump when the thermostat calls for heat? Any help or advice would be great. Thanks..

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    A water temperature sensing switch is called an aquastat. To be safe, you need lots more controls than you are discussing...

    Let's say you have the wood boiler running, but no call for heat. If you just let it sit there, you'll start to generate steam and blow things up! So, you may need to run the circulator constantly, and maybe dump the heat somewhere if the house doesn't need it. Trying to roll your own can get you in trouble with your insurance company, your building inspector, and your life...not counting blowing up your house.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3
    DIY Junior Member mxlord's Avatar
    Join Date
    Dec 2012
    Location
    NY
    Posts
    2

    Default

    I have a aquastat that runs blower to get the fire burning. that is the problem the circulator pump runs all the time and the fire cant keep the water warm enough, it runs about 140 unless i unhook the pump. the water gets to 170 then the blower shuts off and the water stays right around 170. I really just need a thermostat that will run the circulator pump.

  4. #4
    Plumbing Contractor for 49 years johnjh2o1's Avatar
    Join Date
    Aug 2009
    Location
    South*East
    Posts
    1,121

    Default

    The problem you will have is when the thermostat is satisfied and the circulator stops running with the fire burning the boiler will over heat causing a dangerous condition.

    John

Similar Threads

  1. water to air heat exchanger
    By beezer in forum HVAC Heating & Cooling
    Replies: 6
    Last Post: 04-05-2011, 02:27 PM
  2. Helppp..Heat Exchanger quagmire
    By a12548 in forum HVAC Heating & Cooling
    Replies: 5
    Last Post: 05-29-2010, 05:06 PM
  3. Welding a Heat Exchanger
    By molo in forum HVAC Heating & Cooling
    Replies: 8
    Last Post: 09-18-2009, 07:50 PM
  4. potable water heat exchanger
    By leedhouse in forum Remodel Forum & Blog
    Replies: 0
    Last Post: 07-01-2009, 06:59 AM
  5. Heat Exchanger and pump sizing
    By mikeyvon in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 06-02-2008, 09:27 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •