    Default Neutral

    Installed a potters kiln today, 10.5kw, but only split phased (220v).

    I have a red and black hot, green ground, but being the device doesn't receive a neutral, should I disregard it or match it to the ground?

    What is the general rule of neutral coming in contract with ground?

    Why would a 10.5kw device be single phase in the first place?

  2. #2
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Quote Originally Posted by dwindle View Post
    Installed a potters kiln today, 10.5kw, but only split phased (220v).

    I have a red and black hot, green ground, but being the device doesn't receive a neutral, should I disregard it or match it to the ground?

    What is the general rule of neutral coming in contract with ground?

    Why would a 10.5kw device be single phase in the first place?
    The pro electricians will answer up. I am pretty sure the neutral should ONLY ever contact ground at the main panel.

    Most residences, and small commercial properties, are just wired for single phase 220. Plenty of residences that have for example a 60 amp electric heat air handler, on single phase.

  3. #3
    DIY Junior Member Glennsparky's Avatar
    Join Date
    Oct 2012
    Location
    Oviedo, FL near Orlando
    Posts
    22

    Default

    Jimbo is correct. Put a small wire nut on the neutral and don't let it come in contact with anything.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by jimbo View Post
    I am pretty sure the neutral should ONLY ever contact ground at the main panel.
    This is very correct my friend

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,671

    Default

    220/240 v. power is "single phase", not "split phased". If the building only has single phase, then that is how the kiln must be wired. In order to be "three phase" the building would have to be served with three phase power. Then the unit would either need two elements with the "center" leg carrying about 1.75 times the amperage of either element, or multiples of three elements wired so all legs carried the same amperage. Without a 120 v. function the neutral is not needed and should be capped and disregarded.
    Last edited by hj; 12-13-2012 at 06:09 AM.
    Licensed residential and commercial plumber

  6. #6
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    IF the unit has both 120 and 240 functions, it will need the neutral, otherwise, no. Sometimes, like in a stove, there will be a 120vac light, maybe some controls, and possibly a receptacle, so it will need a neutral but the heating elements would be fed from 240vac. No idea on your new kiln whether it needs 120vac and therefore a neutral - it should be clearly spelled out in their installation instructions or be obvious at the junction box where you connect things.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  7. #7
    In the Trades dwindle's Avatar
    Join Date
    Nov 2012
    Location
    North East Pennsylvania
    Posts
    49

    Default

    Quote Originally Posted by jadnashua View Post
    IF the unit has both 120 and 240 functions, it will need the neutral, otherwise, no. Sometimes, like in a stove, there will be a 120vac light, maybe some controls, and possibly a receptacle, so it will need a neutral but the heating elements would be fed from 240vac. No idea on your new kiln whether it needs 120vac and therefore a neutral - it should be clearly spelled out in their installation instructions or be obvious at the junction box where you connect things.
    It does have a low voltage electronic control panel, but I don't know it's input voltage.

    ___

    So, neutral was capped and kiln works fine.

  8. #8
    In the Trades dwindle's Avatar
    Join Date
    Nov 2012
    Location
    North East Pennsylvania
    Posts
    49

    Default

    Quote Originally Posted by hj View Post
    220/240 v. power is "single phase", not "split phased". If the building only has single phase, then that is how the kiln must be wired. In order to be "three phase" the building would have to be served with three phase power. Then the unit would either need two elements with the "center" leg carrying about 1.75 times the amperage of either element, or multiples of three elements wired so all legs carried the same amperage. Without a 120 v. function the neutral is not needed and should be capped and disregarded.
    Maybe I'm using the phrase wrong.

    http://en.wikipedia.org/wiki/Split-phase_electric_power

  9. #9
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    I ( amateur electrical knowledge) have not seen the term split phase used like that. The sparkies will tell us if the industry and/or the electrical code uses that term. Anyway, we are talking about the same thing, whether we call it split or single

  10. #10
    Electrician ActionDave's Avatar
    Join Date
    Feb 2009
    Location
    Colorado
    Posts
    328

    Default

    With a few rare exceptions all power in North America is either single phase or three phase.

    True Split phase power was part of era when electrical power systems were first designed.

  11. #11
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    The only time you will hear split phase is regarding small motors with windings/capacitors that actually split the phase.

Similar Threads

  1. Neutral drops out in circuit.
    By Homeownerinburb in forum Electrical Forum discussion & Blog
    Replies: 14
    Last Post: 01-25-2012, 01:44 PM
  2. Two hot and one neutral
    By pitonyak in forum Electrical Forum discussion & Blog
    Replies: 6
    Last Post: 02-13-2010, 02:52 PM
  3. Subpanel Neutral & Ground On Same Bar?
    By slimjim43 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 06-23-2009, 10:58 AM
  4. Shared neutral
    By beekerc in forum Electrical Forum discussion & Blog
    Replies: 26
    Last Post: 12-11-2008, 12:09 PM
  5. How many neutral conductors do I need?
    By Old Coot in forum Electrical Forum discussion & Blog
    Replies: 37
    Last Post: 08-18-2008, 03:49 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •