Thread: Question about wiring a CT87B Honeywell thermostat

  1. #1
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default Question about wiring a CT87B Honeywell thermostat

    I knew our furnace was not cycling properly, so I decided to move our thermostat to a different wall while also replacing the old T87F Honeywell...and then I discovered what I think is a wiring problem that essentially bypasses the anticipator that had not been set correctly anyway.

    note: The old T87F is presently mounted on a newer base plate nearly identical to the plate for my new CT87B.

    For a 4-wire heating/cooling system like we have, the instructions say to power Rh and Rc...but my picture shows how the current plate is wired differently. So before I follow the directions, does anybody know a reason I should not?

    Name:  ct87b_base.jpg
Views: 1056
Size:  91.1 KB
    Last edited by leejosepho; 12-11-2012 at 01:45 PM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  2. #2
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Correct. Hook it up per directions. Red is power. RH and RC should be jumpered. W is heat. Yellow is cool. Green is fan, IF, they used the normal color code. Verify BOTH ends.

  3. #3
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    I did not verify both ends, but I did follow the directions and it all works well. I am not certain the anticipator had been bypassed by the previous connections, but I do know the furnace now acts like it should. In the past, it would occasionally begin a cycle and then stop abruptly and restart again, and then sometimes also follow a regular cycle with a brief one. But again, now it all works as it should.

    After studying the different wiring diagrams that came with the new thermostat, the previous base that had been on the wall appears to be capable of handling heat and AC along with a heat pump even though the markings on the terminals differ from what the diagram shows for a CT87J setup. Overall, it looks to me like the actual thermostat is the same for all variations and then the model number changes in keeping with the base being used.
    Last edited by leejosepho; 12-13-2012 at 02:14 PM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

Similar Threads

  1. Thermostat wiring question
    By RickM in forum HVAC Heating & Cooling
    Replies: 1
    Last Post: 12-14-2009, 09:42 PM
  2. Old honeywell thermostat a/c fan won't turn off.
    By cpeters in forum HVAC Heating & Cooling
    Replies: 3
    Last Post: 10-01-2009, 07:13 PM
  3. Upgrading Honeywell Thermostat
    By TheOak in forum HVAC Heating & Cooling
    Replies: 13
    Last Post: 10-28-2008, 01:19 PM
  4. Looking for 2 stage honeywell thermostat
    By JOE1934 in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 04-06-2008, 12:30 PM
  5. FielVent Damper/Honeywell S8610 Ignition module wiring question?
    By zippo2 in forum HVAC Heating & Cooling
    Replies: 0
    Last Post: 03-15-2007, 10:50 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •