Shouldn't Light Fixtures Have Bare Grounding Wire Connected?

Users who are viewing this thread

DavidSeon

Member
Messages
47
Reaction score
0
Points
6
Location
MS Gulf Coast
Doing bathroom remodel I notice incoming bare grounding wires of standard 3-wire cable (12ga black, white, bare) is not connected to green screws or green grounding wires supplied with the fixtures, just hanging loose or pushed back in the box. Doing a quick check, I find the same lack of grounding connection at several other fixtures (ceiling light, outdoor porch light, etc), although I haven't checked all of them. In one case, the incoming bare wire is cut back to the insulation and not even available for connection, apparently not used on purpose.

This seems like a no-brainer safety feature to me, and requires such a trivial amount of extra effort, I'm beginning to wonder if I'm missing something. Is there ever a reason NOT to connect the bare grounding wires?

Thanks
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
To: Old Retired Computer Programmer -- Obsolete and loving it
From: an obsolete hobbyist posting in Windows 98 (but I had to use Firefox here)

I would suspect someone was being lazy, so no, you are not missing anything other than a bit of protection in the event of a lightning strike and a GFCI in the bathroom since I do not think one will work at all without a ground wire.
 
Last edited:

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
Is it a metal junction box? I assume it is wired with NM cable (no conduit that could be acting to complete the bonding), correct?

The main purpose of that bare wire is to bond the junction box/fixture. If it was bonded and the box became energized (wire nut came loose and the hot touched the box, or some other fault), that wire would carry current back to the panel (essentially a short between the hot and neutral) and would cause that breaker to trip. Without that bonding, the box/fixture could become energized and could potentially shock someone if they touched it.

As for why they didn't do it, jw or another electrician may be able to answer. Without metallic conduit or another means of bonding, it sounds like they took a shortcut, but perhaps we need more details to tell for sure.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
My question would be what year was the house wired?

My comment would be that the grounding conductor needs to be connected to any grounding conductor in the fixture or the screw on the fixture.

As to the GFCI it will work with or without the grounding conductor.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
FWIW, one accepted use of a GFCI is to swap a 2-prong to a 3-prong (i.e., grounded) receptacle. It makes it more convenient if you have a 3-prong plug, but does not actually provide ground. It is legal if downstream receptacles are fed properly from the load side and it's marked as not having an equipment ground. I'm in the process of doing this at my mother's house as last time I was here, I found some of the 50+ year old receptacles have worn out, and we're not ready to rewire the whole house with grounds, so I'm adding GFCI's and grounded outlets.
 

Cacher_Chick

Test, Don't Guess!
Messages
5,458
Reaction score
213
Points
63
Location
Land of Cheese
Every metal junction/device box should have a threaded ground screw or ground clip installed in the box for connection of the grounding conductor. If the fixture has no ground wire or screw, it was probably made before the mid-60's when it was not a requirement.
 

Kreemoweet

In the Trades
Messages
754
Reaction score
66
Points
28
Location
Seattle. WA
The only legitimate reason I can think of for not properly connecting the Equipment Grounding Conducter in a cable would be if the EGC
was not actually "grounded".
 

DavidSeon

Member
Messages
47
Reaction score
0
Points
6
Location
MS Gulf Coast
Is it a metal junction box? I assume it is wired with NM cable (no conduit that could be acting to complete the bonding), correct?

The main purpose of that bare wire is to bond the junction box/fixture. If it was bonded and the box became energized (wire nut came loose and the hot touched the box, or some other fault), that wire would carry current back to the panel (essentially a short between the hot and neutral) and would cause that breaker to trip. Without that bonding, the box/fixture could become energized and could potentially shock someone if they touched it.

No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.

My question would be what year was the house wired?
Should have mentioned the house was built in 1979 with 12/2 NM-B with ground and 5-15R three-wire grounding receptacles.

The only legitimate reason I can think of for not properly connecting the Equipment Grounding Conducter in a cable would be if the EGC was not actually "grounded".
That's the kind of off-the-wall thing I started worrying about when I saw how consistent they were with not connecting the grounding wires, like maybe they knew something I didn't. Although, the grounding wires were connected to all the outlets on the same circuits, if that means anything.

Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Assuming you can do it safely, open the panel at the breakers and see if they connected the grounds to the ground bus bar. If they did, I'd certainly want to maintain that path for any device that has that provision.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.
Only if the neutral is broken. Like Jim had mentioned in reference to GFCI in a two-wire circuit, the ground can be optional and things will still work as they should.
 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
That is not true. The neutral would not have to be broken for the metal to become energized (if not bonded) or for whether the breaker would trip. It takes 0 current to energize the housing/junction box (would have a potential of say 120v, but no current (think of it as something with infinite resistance)). The breaker has no idea that the housing/box is energized. Bonding the box/fixture would create a dead short back to the panel where the neutrals are connected to the ground bar. Now you are putting that 120v potenial across something of little resistance (just the resistance of the wiring out to the fixture and back). This will cause a large current to flow and that breaker will trip.

A GFCI is another beast. They work by comparing the current on the hot and the neutral. If they are enough out of balance, the GFCI determines that there is current leaking somewhere (like through someone's body) and will trip. It will serve this function with or without the grounding conductor attached.
 

Big2bird

IBEW Electrician
Messages
141
Reaction score
0
Points
16
Location
Anaheim, Ca.
No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.


Should have mentioned the house was built in 1979 with 12/2 NM-B with ground and 5-15R three-wire grounding receptacles.


That's the kind of off-the-wall thing I started worrying about when I saw how consistent they were with not connecting the grounding wires, like maybe they knew something I didn't. Although, the grounding wires were connected to all the outlets on the same circuits, if that means anything.

Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.

No boxes? No grounds connected? Hack job. Every fixture gets a box. Everygound is boded to the box, the mounting strap, and the fixture pig tail.
 

Big2bird

IBEW Electrician
Messages
141
Reaction score
0
Points
16
Location
Anaheim, Ca.
FWIW, one accepted use of a GFCI is to swap a 2-prong to a 3-prong (i.e., grounded) receptacle. It makes it more convenient if you have a 3-prong plug, but does not actually provide ground. It is legal if downstream receptacles are fed properly from the load side and it's marked as not having an equipment ground. I'm in the process of doing this at my mother's house as last time I was here, I found some of the 50+ year old receptacles have worn out, and we're not ready to rewire the whole house with grounds, so I'm adding GFCI's and grounded outlets.
The first receptacle in the circuit string after it leaves the panel is sufficient. The rest can be normal 3 prong receptacles fed thru the first GFCI in the string. The just must be marked as such.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.


You can measure the resistance from the unconnected wire to neutral , it should be near 0 ohms if it is connected at the other end.
 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
^But, remember to cut the main breaker before you do this. The neutral could have voltage on it from other devices on that circuit. Voltages do not play nice with your meter when checking for ohms. :)

Turning off only the breaker that this circuit is on should be good enough for this test, but I would do the main, just in case. With the other issues you have found, you don't know if they tied neutrals from other circuits together (outside the panel) or did any other funny stuff.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Not a bad idea nukeman.

I always check for voltage before trying to use the ohm meter on unknown wires.

Turning off the power may be safer.

I also use a light bulb for testing, but JW says that is a no-no.

It is best to be safe when playing with electricity.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
It is best to have a Ground even when using a GFI.

The GFI will work without a ground, But if a ground is connected and you have a Appliance fault, The GFI and maybe the breaker will trip.

That is better than a persons body being needed to make a ground fault trip.
 

DavidSeon

Member
Messages
47
Reaction score
0
Points
6
Location
MS Gulf Coast
Just to be safe I cut the power at both the outdoor main panel and the indoor subpanel before removing the subpanel cover

Inside Breaker Panel.jpg

I can see the bare grounding conductors fastened to the ground bar on the right, and the white neutrals all connected to the neutral bar on the bottom. The grounds and neutrals are not connected together in the subpanel, but my understanding is they are bonded together at the outdoor main panel. I don't understand why the cable coming in at the bottom has a green conductor instead of a bare wire, but maybe just what they had on hand?

This may be goofy but just to satisfy myself, I connected a 25 foot length of zipcord to the ground rod outdoors by the main panel, and brought the other end inside to the unconnected bathroom fixture wiring. I get 1.2 ohms resistance from the bare gounding conductor to the ground rod, and 1.3 ohms from the neutral to the rod; the zipcord reads 1 ohm by itself.

I'm thinking the main wiring for the panels out to the transformer is correct but if I'm misinterpreting something, please let me know. Because of the issues I've seen, I'm planning to check all of the fixture wiring connections; apparently they used hacks for that.

Thanks for all the help.
Dave
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Your measurement sounds about correct.

There is nothing wrong with Green.

The wire just cost more, in most cases.

The Ground does not have to be Bare.
 