Thread: Shouldn't Light Fixtures Have Bare Grounding Wire Connected?

  1. #1
    DIY Member DavidSeon's Avatar
    Join Date
    Jul 2012
    Location
    MS Gulf Coast
    Posts
    47

    Default Shouldn't Light Fixtures Have Bare Grounding Wire Connected?

    Doing bathroom remodel I notice incoming bare grounding wires of standard 3-wire cable (12ga black, white, bare) is not connected to green screws or green grounding wires supplied with the fixtures, just hanging loose or pushed back in the box. Doing a quick check, I find the same lack of grounding connection at several other fixtures (ceiling light, outdoor porch light, etc), although I haven't checked all of them. In one case, the incoming bare wire is cut back to the insulation and not even available for connection, apparently not used on purpose.

    This seems like a no-brainer safety feature to me, and requires such a trivial amount of extra effort, I'm beginning to wonder if I'm missing something. Is there ever a reason NOT to connect the bare grounding wires?

    Thanks
    Old Retired Computer Programmer
    Obsolete and loving it

  2. #2
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    To: Old Retired Computer Programmer -- Obsolete and loving it
    From: an obsolete hobbyist posting in Windows 98 (but I had to use Firefox here)

    I would suspect someone was being lazy, so no, you are not missing anything other than a bit of protection in the event of a lightning strike and a GFCI in the bathroom since I do not think one will work at all without a ground wire.
    Last edited by leejosepho; 12-11-2012 at 02:13 PM.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  3. #3
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    Is it a metal junction box? I assume it is wired with NM cable (no conduit that could be acting to complete the bonding), correct?

    The main purpose of that bare wire is to bond the junction box/fixture. If it was bonded and the box became energized (wire nut came loose and the hot touched the box, or some other fault), that wire would carry current back to the panel (essentially a short between the hot and neutral) and would cause that breaker to trip. Without that bonding, the box/fixture could become energized and could potentially shock someone if they touched it.

    As for why they didn't do it, jw or another electrician may be able to answer. Without metallic conduit or another means of bonding, it sounds like they took a shortcut, but perhaps we need more details to tell for sure.

  4. #4
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    My question would be what year was the house wired?

    My comment would be that the grounding conductor needs to be connected to any grounding conductor in the fixture or the screw on the fixture.

    As to the GFCI it will work with or without the grounding conductor.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,446

    Default

    FWIW, one accepted use of a GFCI is to swap a 2-prong to a 3-prong (i.e., grounded) receptacle. It makes it more convenient if you have a 3-prong plug, but does not actually provide ground. It is legal if downstream receptacles are fed properly from the load side and it's marked as not having an equipment ground. I'm in the process of doing this at my mother's house as last time I was here, I found some of the 50+ year old receptacles have worn out, and we're not ready to rewire the whole house with grounds, so I'm adding GFCI's and grounded outlets.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,161

    Default

    Every metal junction/device box should have a threaded ground screw or ground clip installed in the box for connection of the grounding conductor. If the fixture has no ground wire or screw, it was probably made before the mid-60's when it was not a requirement.

  7. #7
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    The only legitimate reason I can think of for not properly connecting the Equipment Grounding Conducter in a cable would be if the EGC
    was not actually "grounded".

  8. #8
    DIY Member DavidSeon's Avatar
    Join Date
    Jul 2012
    Location
    MS Gulf Coast
    Posts
    47

    Default

    Quote Originally Posted by nukeman View Post
    Is it a metal junction box? I assume it is wired with NM cable (no conduit that could be acting to complete the bonding), correct?

    The main purpose of that bare wire is to bond the junction box/fixture. If it was bonded and the box became energized (wire nut came loose and the hot touched the box, or some other fault), that wire would carry current back to the panel (essentially a short between the hot and neutral) and would cause that breaker to trip. Without that bonding, the box/fixture could become energized and could potentially shock someone if they touched it.
    No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.

    Quote Originally Posted by jwelectric View Post
    My question would be what year was the house wired?
    Should have mentioned the house was built in 1979 with 12/2 NM-B with ground and 5-15R three-wire grounding receptacles.

    Quote Originally Posted by kreemoweet View Post
    The only legitimate reason I can think of for not properly connecting the Equipment Grounding Conducter in a cable would be if the EGC was not actually "grounded".
    That's the kind of off-the-wall thing I started worrying about when I saw how consistent they were with not connecting the grounding wires, like maybe they knew something I didn't. Although, the grounding wires were connected to all the outlets on the same circuits, if that means anything.

    Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.
    Old Retired Computer Programmer
    Obsolete and loving it

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,446

    Default

    Assuming you can do it safely, open the panel at the breakers and see if they connected the grounds to the ground bus bar. If they did, I'd certainly want to maintain that path for any device that has that provision.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by DavidSeon View Post
    No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.
    Only if the neutral is broken. Like Jim had mentioned in reference to GFCI in a two-wire circuit, the ground can be optional and things will still work as they should.
    "Great minds discuss ideas, average minds discuss events and small minds discuss people." --Eleanor Roosevelt

  11. #11
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    That is not true. The neutral would not have to be broken for the metal to become energized (if not bonded) or for whether the breaker would trip. It takes 0 current to energize the housing/junction box (would have a potential of say 120v, but no current (think of it as something with infinite resistance)). The breaker has no idea that the housing/box is energized. Bonding the box/fixture would create a dead short back to the panel where the neutrals are connected to the ground bar. Now you are putting that 120v potenial across something of little resistance (just the resistance of the wiring out to the fixture and back). This will cause a large current to flow and that breaker will trip.

    A GFCI is another beast. They work by comparing the current on the hot and the neutral. If they are enough out of balance, the GFCI determines that there is current leaking somewhere (like through someone's body) and will trip. It will serve this function with or without the grounding conductor attached.

  12. #12
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by DavidSeon View Post
    No boxes for the vanity fixtures, they just punched a hole in the drywall for the cable. I picked up a couple of plastic ceiling boxes with hanger bars for making a neater installation of the new fixtures. My concern was, as you described, if the exposed metal of the fixture became energized, the breaker wouldn't trip if the grounding wire wasn't connected.


    Should have mentioned the house was built in 1979 with 12/2 NM-B with ground and 5-15R three-wire grounding receptacles.


    That's the kind of off-the-wall thing I started worrying about when I saw how consistent they were with not connecting the grounding wires, like maybe they knew something I didn't. Although, the grounding wires were connected to all the outlets on the same circuits, if that means anything.

    Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.
    No boxes? No grounds connected? Hack job. Every fixture gets a box. Everygound is boded to the box, the mounting strap, and the fixture pig tail.

  13. #13
    IBEW Electrician big2bird's Avatar
    Join Date
    Sep 2012
    Location
    Anaheim, Ca.
    Posts
    141

    Default

    Quote Originally Posted by jadnashua View Post
    FWIW, one accepted use of a GFCI is to swap a 2-prong to a 3-prong (i.e., grounded) receptacle. It makes it more convenient if you have a 3-prong plug, but does not actually provide ground. It is legal if downstream receptacles are fed properly from the load side and it's marked as not having an equipment ground. I'm in the process of doing this at my mother's house as last time I was here, I found some of the 50+ year old receptacles have worn out, and we're not ready to rewire the whole house with grounds, so I'm adding GFCI's and grounded outlets.
    The first receptacle in the circuit string after it leaves the panel is sufficient. The rest can be normal 3 prong receptacles fed thru the first GFCI in the string. The just must be marked as such.

  14. #14
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,662

    Default

    Quote Originally Posted by DavidSeon View Post
    Is there a way to verify that the grounding path is adequate with my Fluke meter, resistance maybe? Have a lot of experience troubleshooting, voltage and signal tracing on live military electronic equipment, just not building wiring. I'm comfortable that I can keep myself safe, or at least know when I'm not.

    You can measure the resistance from the unconnected wire to neutral , it should be near 0 ohms if it is connected at the other end.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

  15. #15
    Nuclear Engineer nukeman's Avatar
    Join Date
    Nov 2009
    Location
    VA
    Posts
    696

    Default

    ^But, remember to cut the main breaker before you do this. The neutral could have voltage on it from other devices on that circuit. Voltages do not play nice with your meter when checking for ohms.

    Turning off only the breaker that this circuit is on should be good enough for this test, but I would do the main, just in case. With the other issues you have found, you don't know if they tied neutrals from other circuits together (outside the panel) or did any other funny stuff.

Similar Threads

  1. New blogger. How to wire a fan with light?
    By Molly d in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 11-26-2012, 10:18 AM
  2. ? Connected Gas Dryer with Gas Boiler on same line-Now Pilot Light turns off ?
    By 87vertgt in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 15
    Last Post: 10-16-2011, 08:25 AM
  3. Ungrounded Light Fixtures
    By bigbubba in forum Electrical Forum discussion & Blog
    Replies: 4
    Last Post: 06-16-2010, 04:47 PM
  4. J-type halogen light fixtures
    By Kiko in forum Electrical Forum discussion & Blog
    Replies: 3
    Last Post: 10-25-2009, 11:11 AM
  5. heavy gauge bare copper wire
    By solutions in forum Electrical Forum discussion & Blog
    Replies: 2
    Last Post: 03-26-2008, 07:11 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •